Question, If a sub-panel is being feed from a breaker in a main-panel thru a square wireway,can branch circuits wires be in the same square wireway as the wires feeding the sub-panel? Boomer

#7717 02/18/02 08:14 AM
Joined: Oct 2000
Posts: 5,392
S
Member
Boomer,
i see no violation in feeders & branch circuits occuping the same space....

#7718 02/18/02 08:19 AM
Joined: Jul 2001
Posts: 311
F
Member
If your question is: Can feeder conductors be installed the same raceway as branch circuit conductors, the answer is yes.

Don't forget to derate if applicable.

#7719 02/18/02 08:17 PM
Joined: Feb 2002
Posts: 840
C
Member
Check out 230-7. Feeders and branch circuits cannot occupy the same space as service conductors.
So, there is no violation as long as there are no service conductors in the wireway you mentioned. Since you metioned that this is a sub-panel, I dont see a problem.

See page 101 of Mike Holt's "Understanding the NEC 1999" if you have it. It explains this sitation really well.

[This message has been edited by CTwireman (edited 02-18-2002).]


Peter
#7720 02/19/02 09:24 AM
Joined: Dec 2000
Posts: 4,291
Member
See 362-5 or 376.22
If you exceed 30 current carrying conductors, you'll have to derate to 40% up to 40 conductors, or 35% beyond that.
Up to 30 conductors, derating is not applicable.
I'm the big "Gutter Complainer" of the group [Linked Image]
Edited 'cause I used the wrong article.[foot in mouth] Thanks, Joe![/foot in mouth]



[This message has been edited by electure (edited 02-19-2002).]

#7721 02/21/02 07:06 PM
Joined: Aug 2001
Posts: 329
S
Member
Well Boomer, if we can't ...let's just say there are "several" illegal sub panels in the DC/VA area. [Linked Image]


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
dougwells
dougwells
kamloops BC Canada
Posts: 1,158
Joined: May 2003
Top Posters(30 Days)
BigB 3
triple 2
Popular Topics(Views)
305,039 Are you busy
233,457 Re: Forum
218,144 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5