Sub-panel #7716 02/17/02 10:27 PM
Joined: Feb 2002
Posts: 5
B
Boomer Offline OP
Junior Member
Question, If a sub-panel is being feed from a breaker in a main-panel thru a square wireway,can branch circuits wires be in the same square wireway as the wires feeding the sub-panel? Boomer

Work Gear for Electricians and the Trades
Re: Sub-panel #7717 02/18/02 08:14 AM
Joined: Oct 2000
Posts: 5,389
S
sparky Offline
Member
Boomer,
i see no violation in feeders & branch circuits occuping the same space....

Re: Sub-panel #7718 02/18/02 08:19 AM
Joined: Jul 2001
Posts: 311
F
Frank Cinker Offline
Member
If your question is: Can feeder conductors be installed the same raceway as branch circuit conductors, the answer is yes.

Don't forget to derate if applicable.

Re: Sub-panel #7719 02/18/02 08:17 PM
Joined: Feb 2002
Posts: 840
C
CTwireman Offline
Member
Check out 230-7. Feeders and branch circuits cannot occupy the same space as service conductors.
So, there is no violation as long as there are no service conductors in the wireway you mentioned. Since you metioned that this is a sub-panel, I dont see a problem.

See page 101 of Mike Holt's "Understanding the NEC 1999" if you have it. It explains this sitation really well.

[This message has been edited by CTwireman (edited 02-18-2002).]


Peter
Re: Sub-panel #7720 02/19/02 09:24 AM
Joined: Dec 2000
Posts: 4,283
electure Offline
Member
See 362-5 or 376.22
If you exceed 30 current carrying conductors, you'll have to derate to 40% up to 40 conductors, or 35% beyond that.
Up to 30 conductors, derating is not applicable.
I'm the big "Gutter Complainer" of the group [Linked Image]
Edited 'cause I used the wrong article.[foot in mouth] Thanks, Joe![/foot in mouth]



[This message has been edited by electure (edited 02-19-2002).]

Re: Sub-panel #7721 02/21/02 07:06 PM
Joined: Aug 2001
Posts: 329
S
Steve Miller Offline
Member
Well Boomer, if we can't ...let's just say there are "several" illegal sub panels in the DC/VA area. [Linked Image]


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 8
NORCAL 3
Popular Topics(Views)
269,954 Are you busy
204,379 Re: Forum
192,598 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3