Sub-panel #7716
02/17/02 10:27 PM
02/17/02 10:27 PM
B
Boomer  Offline OP
Junior Member
Joined: Feb 2002
Posts: 5
Question, If a sub-panel is being feed from a breaker in a main-panel thru a square wireway,can branch circuits wires be in the same square wireway as the wires feeding the sub-panel? Boomer

Work Gear for Electricians and the Trades
Re: Sub-panel #7717
02/18/02 08:14 AM
02/18/02 08:14 AM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,372
Boomer,
i see no violation in feeders & branch circuits occuping the same space....

Re: Sub-panel #7718
02/18/02 08:19 AM
02/18/02 08:19 AM
F
Frank Cinker  Offline
Member
Joined: Jul 2001
Posts: 311
Pennsylvania
If your question is: Can feeder conductors be installed the same raceway as branch circuit conductors, the answer is yes.

Don't forget to derate if applicable.

Re: Sub-panel #7719
02/18/02 08:17 PM
02/18/02 08:17 PM
C
CTwireman  Offline
Member
Joined: Feb 2002
Posts: 840
Connecticut, USA
Check out 230-7. Feeders and branch circuits cannot occupy the same space as service conductors.
So, there is no violation as long as there are no service conductors in the wireway you mentioned. Since you metioned that this is a sub-panel, I dont see a problem.

See page 101 of Mike Holt's "Understanding the NEC 1999" if you have it. It explains this sitation really well.

[This message has been edited by CTwireman (edited 02-18-2002).]


Peter
Re: Sub-panel #7720
02/19/02 09:24 AM
02/19/02 09:24 AM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,280
Fullerton, CA USA
See 362-5 or 376.22
If you exceed 30 current carrying conductors, you'll have to derate to 40% up to 40 conductors, or 35% beyond that.
Up to 30 conductors, derating is not applicable.
I'm the big "Gutter Complainer" of the group [Linked Image]
Edited 'cause I used the wrong article.[foot in mouth] Thanks, Joe![/foot in mouth]



[This message has been edited by electure (edited 02-19-2002).]

Re: Sub-panel #7721
02/21/02 07:06 PM
02/21/02 07:06 PM
S
Steve Miller  Offline
Member
Joined: Aug 2001
Posts: 329
Bruceton Mills, WV
Well Boomer, if we can't ...let's just say there are "several" illegal sub panels in the DC/VA area. [Linked Image]


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
watersparkfalls
watersparkfalls
Washington...Not DC
Posts: 233
Joined: March 2005
Show All Member Profiles 
Top Posters(30 Days)
Khombo 2
Popular Topics(Views)
255,737 Are you busy
191,702 Re: Forum
181,482 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.028s Queries: 14 (0.006s) Memory: 0.9762 MB (Peak: 1.1231 MB) Zlib enabled. Server Time: 2019-06-18 12:57:49 UTC