I was told that for the new 2005 code that (NM) romex for applainaces ie; water heater, ac disconnect, dryer must now be in 3 wire. Is this true and if so can some one please state a code # reference. I am racking my head trying to find this but have been unable.
|
|
|
|
Joined: May 2002
Posts: 1,716
Member
|
There is no such NEC requirement, a 2 conductor with ground is all that is needed
Roger
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
You can not feed a 240/120 dryer with a 3 wire.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Jan 2005
Posts: 5,445 Likes: 2
Cat Servant Member
|
One must ask the question right, to get the answer right :-)
At one time- not so long ago- it was the practice to "ground" the case of a range or clothes dryer by bonding it to the third wire- which also served as the "neutral" for any 110 loads the appliance might have had.
This is no longer allowed on NEW dryers and ranges, nor is it allowed to run NEW circuits this way. Section 250.140 is the place to start reading...
So, today, we no longer bond the case to the "neutral" wire. We run an additional wire to serve as the ground wire.
If an appliance has no 110v loads, then the third prong of the plug is a true "ground" prong.
|
|
|
|
Joined: Aug 2004
Posts: 186
OP
Member
|
so renosteinke then would you or wouldn't you use 3 wire?
i have done several ovens micro/convection over the last year where they came with a set up of a black , a red, a neutral and a ground? for a 220 set up 30 amp and man i must say i love this place that was quick 3 responces in no time. Gotta love it thanks kenny
|
|
|
|
Joined: May 2002
Posts: 1,716
Member
|
Whoa, I only (stopped reading at) read "water heater and ac disconnect", shame on me. Iwire and John are correct, on 120/240v appliances, a three insulated conductor with equipment grounding conductor wiring method must be used. Roger
|
|
|
|
Joined: Aug 2004
Posts: 186
OP
Member
|
but john says yes and i wire says no?
|
|
|
|
Joined: Jan 2002
Posts: 1,457
Member
|
Two hots, one neutral and one ground (very untechnical I know) require two hots, one neutral and one ground feeding it.
|
|
|
|
Joined: May 2002
Posts: 1,716
Member
|
NJ Wireman, actually I think John and Iwire are saying the same thing, Iwire said You can not feed a 240/120 dryer with a 3 wire. I think Iwire means there must be four conductors John said So, today, we no longer bond the case to the "neutral" wire. We run an additional wire to serve as the ground wire. Roger [This message has been edited by Roger (edited 12-12-2005).]
|
|
|
|
Joined: Aug 2004
Posts: 186
OP
Member
|
I see i thought when he said three wire, i mis understood. I thank all for their help.
|
|
|