ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
UL 508A SPACING
by ale348 - 03/29/24 01:09 AM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (ale348), 302 guests, and 14 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 2 1 2
#59656 12/12/05 08:42 PM
Joined: Aug 2004
Posts: 186
N
Member
I was told that for the new 2005 code that (NM) romex for applainaces ie; water heater, ac disconnect, dryer must now be in 3 wire. Is this true and if so can some one please state a code # reference. I am racking my head trying to find this but have been unable.

Joined: May 2002
Posts: 1,716
R
Member
There is no such NEC requirement, a 2 conductor with ground is all that is needed

Roger

Joined: Jan 2003
Posts: 4,391
I
Moderator
You can not feed a 240/120 dryer with a 3 wire.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Joined: Jan 2005
Posts: 5,445
Likes: 2
Cat Servant
Member
One must ask the question right, to get the answer right :-)

At one time- not so long ago- it was the practice to "ground" the case of a range or clothes dryer by bonding it to the third wire- which also served as the "neutral" for any 110 loads the appliance might have had.

This is no longer allowed on NEW dryers and ranges, nor is it allowed to run NEW circuits this way. Section 250.140 is the place to start reading...

So, today, we no longer bond the case to the "neutral" wire. We run an additional wire to serve as the ground wire.

If an appliance has no 110v loads, then the third prong of the plug is a true "ground" prong.

Joined: Aug 2004
Posts: 186
N
Member
so renosteinke
then would you or wouldn't you use 3 wire?

i have done several ovens micro/convection over the last year where they came with a set up of a black , a red, a neutral and a ground? for a 220 set up 30 amp and man i must say i love this place that was quick 3 responces in no time. Gotta love it thanks kenny

Joined: May 2002
Posts: 1,716
R
Member
Whoa, I only (stopped reading at) read "water heater and ac disconnect", shame on me. [Linked Image]

Iwire and John are correct, on 120/240v appliances, a three insulated conductor with equipment grounding conductor wiring method must be used.


Roger

Joined: Aug 2004
Posts: 186
N
Member
but john says yes and i wire says no?

Joined: Jan 2002
Posts: 1,457
E
Member
Two hots, one neutral and one ground (very untechnical I know) require two hots, one neutral and one ground feeding it.

Joined: May 2002
Posts: 1,716
R
Member
NJ Wireman, actually I think John and Iwire are saying the same thing,

Iwire said
Quote
You can not feed a 240/120 dryer with a 3 wire.

I think Iwire means there must be four conductors

John said
Quote
So, today, we no longer bond the case to the "neutral" wire. We run an additional wire to serve as the ground wire.

Roger



[This message has been edited by Roger (edited 12-12-2005).]

Joined: Aug 2004
Posts: 186
N
Member
I see i thought when he said three wire, i mis understood. I thank all for their help.