ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 267 guests, and 17 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#47062 01/07/05 07:57 PM
Joined: Mar 2002
Posts: 125
S
Member
Does any know how to calculate the ize per room. Say 12x14 ft. Thanks

Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

#47063 01/07/05 08:11 PM
Joined: Jan 2003
Posts: 33
C
Member
Rule of thumb is 10 watts per sq foot of floor area, based on an 8 foot ceiling height. 12 x 14 room is 168 sq ft, so that would be 1.68 kw. one foot of baseboard heat is typically 250 watts, so that would be 6.72 feet (have to round up of course) of baseboard heat required.

#47064 01/07/05 08:53 PM
Joined: Mar 2002
Posts: 125
S
Member
Thanks i have only replaced existing nerver install new.


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5