Does any know how to calculate the ize per room. Say 12x14 ft. Thanks

Horizontal Ad
#47063 01/07/05 08:11 PM
Joined: Jan 2003
Posts: 33
C
Member
Rule of thumb is 10 watts per sq foot of floor area, based on an 8 foot ceiling height. 12 x 14 room is 168 sq ft, so that would be 1.68 kw. one foot of baseboard heat is typically 250 watts, so that would be 6.72 feet (have to round up of course) of baseboard heat required.

#47064 01/07/05 08:53 PM
Joined: Mar 2002
Posts: 125
S
Member
Thanks i have only replaced existing nerver install new.