gas range igniters #40199 07/14/04 11:43 AM
Joined: Jan 2002
Posts: 59
C
Creighton Offline OP
Member
Some gas ranges and gas cooking tops require electricity for the igniters. Question: do you hard wire these, or provide a receptacle?
If a receptacle, what is the height above the floor?
Creighton

Work Gear for Electricians and the Trades
Re: gas range igniters #40200 07/14/04 11:53 AM
Joined: Feb 2004
Posts: 1,432
Lostazhell Offline
Member
Creighton,
Every cooktop I've seen with igniters is cord & plug connected... the igniters draw very little energy, as the 25W light in the over also... I typically place the outlet +18"AFF behind the unit...

-Randy

PS... I've come across a couple gas ranges with "browning elements" in them, which are electric. The ones I saw required a dedicated circuit per mfr instructions (1750W 120V).
Just something to keep an eye open for [Linked Image]

Re: gas range igniters #40201 07/14/04 07:44 PM
Joined: Mar 2003
Posts: 21
C
CharlieK Offline
Member
Creighton, I once had a problem with the range ignitor tripping the GFI I had it on. Inspector said GFI was not needed.

Re: gas range igniters #40202 07/14/04 08:35 PM
Joined: Nov 2002
Posts: 558
G
ga.sparky56 Offline
Member
We do ours pretty much like Randy.

A recep about 18 or 20" above the floor.


Russell

Re: gas range igniters #40203 07/14/04 10:53 PM
Joined: Jun 2003
Posts: 1,143
D
DougW Offline
Member
I've had requests to mount the receptacles 24" AFF for ease of access.

Re: gas range igniters #40204 07/15/04 02:31 AM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
Another thing to watch for...
Trim kits, if the range requires any tools to remove, the receptical is no longer accessable, so you should put it a cabinet to the left or right. Some will specify which one.


Mark Heller
"Well - I oughta....." -Jackie Gleason
Re: gas range igniters #40205 07/15/04 10:51 AM
Joined: Jan 2002
Posts: 59
C
Creighton Offline OP
Member
Thanks to all. In a nearby jurisdiction an installer wanted to put the receptacle on the wall above the gas range. The only thing we could find in the NEC to prohibit it was 110.11 where it speaks of excessive temperatures.

Re: gas range igniters #40206 07/15/04 05:42 PM
Joined: Jan 2002
Posts: 1,457
E
Electricmanscott Offline
Member
E57 where is the requirement for the receptacles to be accessible? You can put them behind dishwashers, built in microwaves, trash compactors, etc. Why not a built in stove?

Re: gas range igniters #40207 07/17/04 06:08 PM
Joined: Jul 2004
Posts: 5
F
fiddler Offline
Junior Member
Never checked it out but the amp draw of

these Igniters seem to be high as they will

not fire if you're having low volatge.Seen

this happen often.

Re: gas range igniters #40208 07/17/04 06:30 PM
Joined: Dec 2002
Posts: 308
E
Edward Offline
Member
Accessible (As applied to equipment)Admitting close approach:not gurded by locked doors, elevation or other effective means.

Accessible readily: Capable of being reached quickly for operation, renewal or inspection without requiring those to whom ready access is requisite to climb over or remove obstacles or to resort to portable ladders, chairs, etc.

So according to the above explanation i would consider behind dishwasher,built-in microwave and a compactor not readily accessible.

Edward

[This message has been edited by Edward (edited 07-17-2004).]


Thanks
Edward
Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
watersparkfalls
watersparkfalls
Washington...Not DC
Posts: 236
Joined: March 2005
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
271,060 Are you busy
205,042 Re: Forum
193,167 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3