Nice point made there!
You must be careful to think of all possible metallic paths, not just the raceway the conductors are in.
Water and gas pipes, phone and cable TV wires, it is possible even a metal fence might run between two metal structures creating a parallel path for neutral current.
Often over-looked items....
what about 250 32 d
trekkie76,
250.32(D) only applies when exceptions 1 or 2 of 225.32 are met (the 225.31 in some printings of the NEC is a misprint - see the errata). Those exceptions will not apply to the situation you describe, so 250.32(D) will not come into play. In addition to the main disconnect at the pole, 225.32 will require a disconnecting means located at the house.
Thanks e57. [Linked Image]
Bob
225-32 refers to placement of the disconnecting means on the premise. those exceptions don't nessasarly have to be applied. So, 250-32d says that as long as the placement(location)of the disconnect conforms to 225-32, the following conditions shall be met:
1. the connection of the grounded conductor to the grounding electrode at the seperate building shall NOT be made.
2. An equipment grounding conductor for grounding any non-current carrying ewuipment shall be run with the circuit conductors, and bonded to the grounding electrode.
3. the bonding shall be done in a panelboard, j- box.
With the service disconnect on the pole(1st building) feeding the house( 2nd building), the disconnect is outside the buildings, satisfying 225-32, wouldn't this situation be called" disconnecting means located in Seperate Building or structure on the same premises" ?