trekkie76,
250.32(D) only applies when exceptions 1 or 2 of 225.32 are met (the 225.31 in some printings of the NEC is a misprint - see the errata). Those exceptions will not apply to the situation you describe, so 250.32(D) will not come into play. In addition to the main disconnect at the pole, 225.32 will require a disconnecting means located at the house.