ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 192 guests, and 7 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#219396 06/04/18 06:51 PM
Joined: Mar 2004
Posts: 947
T
twh Offline OP
Member
I have a friend who owns a house in Montana. His fridge is on an AFCI breaker that trips every time they have a power failure. In Canada, we don't AFCI fridge plugs. Do you not have an exception for fridges?

Work Gear for Electricians and the Trades

Workgear for Electricians

twh #219397 06/04/18 08:41 PM
Joined: Jul 2004
Posts: 10,053
Likes: 40
G
Member
Short answer no.


Greg Fretwell
twh #219398 06/04/18 10:41 PM
Joined: Mar 2004
Posts: 947
T
twh Offline OP
Member
Are you allowed to install an AFCI in a box beside the panel. I wonder if it's the make of the breaker that is the problem.

twh #219399 06/05/18 04:47 PM
Joined: Jul 2004
Posts: 10,053
Likes: 40
G
Member
There are rules about how to do it but generally yes you can use a device type AFCI in the first outlet on a branch circuit if it is less than 50' away (wire length). The easiest way to comply is to use a piece of MC cable between the box and the panel. If it is a straight shot you could even use a piece of EMT or a close nipple for a side by side install. It just has to be in metal.
Before I did all of that I would try it on a GFCI only circuit. If that trips look inward toward the fridge. It is not uncommon for old fridges with bad compressors to trip GFCIs.


Greg Fretwell
Joined: Mar 2004
Posts: 947
T
twh Offline OP
Member
Originally Posted by gfretwell
Before I did all of that I would try it on a GFCI only circuit. If that trips look inward toward the fridge. It is not uncommon for old fridges with bad compressors to trip GFCIs.
Good idea!


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5