ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
Positive Ground on 125 VDC Station Batteries
by The Watt Doctor. 05/23/19 08:55 AM
2020 is at the printers.
by gfretwell. 05/22/19 10:11 AM
Chinese wire symbols?
by Texas_Ranger. 05/19/19 03:09 PM
Pool - Daisy chained GFCI
by gfretwell. 05/18/19 01:30 PM
110.26 working clearances
by HotLine1. 05/14/19 02:08 PM
New in the Gallery:
What is this for?
Plug terminals
Who's Online Now
0 registered members (), 9 guests, and 15 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
AFCI on Fridges #219396
06/04/18 06:51 PM
06/04/18 06:51 PM
T
twh  Offline OP
Member
Joined: Mar 2004
Posts: 947
Regina, Sask.
I have a friend who owns a house in Montana. His fridge is on an AFCI breaker that trips every time they have a power failure. In Canada, we don't AFCI fridge plugs. Do you not have an exception for fridges?

2017 / 2014 NEC & Related Books and Study Guides
Re: AFCI on Fridges [Re: twh] #219397
06/04/18 08:41 PM
06/04/18 08:41 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,362
Estero,Fl,usa
Short answer no.


Greg Fretwell
Re: AFCI on Fridges [Re: twh] #219398
06/04/18 10:41 PM
06/04/18 10:41 PM
T
twh  Offline OP
Member
Joined: Mar 2004
Posts: 947
Regina, Sask.
Are you allowed to install an AFCI in a box beside the panel. I wonder if it's the make of the breaker that is the problem.

Re: AFCI on Fridges [Re: twh] #219399
06/05/18 04:47 PM
06/05/18 04:47 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,362
Estero,Fl,usa
There are rules about how to do it but generally yes you can use a device type AFCI in the first outlet on a branch circuit if it is less than 50' away (wire length). The easiest way to comply is to use a piece of MC cable between the box and the panel. If it is a straight shot you could even use a piece of EMT or a close nipple for a side by side install. It just has to be in metal.
Before I did all of that I would try it on a GFCI only circuit. If that trips look inward toward the fridge. It is not uncommon for old fridges with bad compressors to trip GFCIs.


Greg Fretwell
Re: AFCI on Fridges [Re: gfretwell] #219400
06/05/18 10:25 PM
06/05/18 10:25 PM
T
twh  Offline OP
Member
Joined: Mar 2004
Posts: 947
Regina, Sask.
Originally Posted by gfretwell
Before I did all of that I would try it on a GFCI only circuit. If that trips look inward toward the fridge. It is not uncommon for old fridges with bad compressors to trip GFCIs.
Good idea!


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
electure
electure
Fullerton, CA USA
Posts: 4,280
Joined: December 2000
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
255,147 Are you busy
191,239 Re: Forum
180,987 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.028s Queries: 15 (0.005s) Memory: 0.9689 MB (Peak: 1.1098 MB) Zlib enabled. Server Time: 2019-05-23 19:02:13 UTC