AFCI on Fridges #219396
06/04/18 06:51 PM
06/04/18 06:51 PM
T
twh  Offline OP
Member
Joined: Mar 2004
Posts: 947
Regina, Sask.
I have a friend who owns a house in Montana. His fridge is on an AFCI breaker that trips every time they have a power failure. In Canada, we don't AFCI fridge plugs. Do you not have an exception for fridges?

2017 / 2014 NEC & Related Books and Study Guides
Re: AFCI on Fridges [Re: twh] #219397
06/04/18 08:41 PM
06/04/18 08:41 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,298
Estero,Fl,usa
Short answer no.


Greg Fretwell
Re: AFCI on Fridges [Re: twh] #219398
06/04/18 10:41 PM
06/04/18 10:41 PM
T
twh  Offline OP
Member
Joined: Mar 2004
Posts: 947
Regina, Sask.
Are you allowed to install an AFCI in a box beside the panel. I wonder if it's the make of the breaker that is the problem.

Re: AFCI on Fridges [Re: twh] #219399
06/05/18 04:47 PM
06/05/18 04:47 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,298
Estero,Fl,usa
There are rules about how to do it but generally yes you can use a device type AFCI in the first outlet on a branch circuit if it is less than 50' away (wire length). The easiest way to comply is to use a piece of MC cable between the box and the panel. If it is a straight shot you could even use a piece of EMT or a close nipple for a side by side install. It just has to be in metal.
Before I did all of that I would try it on a GFCI only circuit. If that trips look inward toward the fridge. It is not uncommon for old fridges with bad compressors to trip GFCIs.


Greg Fretwell
Re: AFCI on Fridges [Re: gfretwell] #219400
06/05/18 10:25 PM
06/05/18 10:25 PM
T
twh  Offline OP
Member
Joined: Mar 2004
Posts: 947
Regina, Sask.
Originally Posted by gfretwell
Before I did all of that I would try it on a GFCI only circuit. If that trips look inward toward the fridge. It is not uncommon for old fridges with bad compressors to trip GFCIs.
Good idea!


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
The_Lightman
The_Lightman
Orlando, Fl, USA
Posts: 49
Joined: August 2001
Show All Member Profiles 
Top Posters(30 Days)
sparky 11
Popular Topics(Views)
250,540 Are you busy
188,098 Re: Forum
177,730 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.021s Queries: 15 (0.003s) Memory: 0.9690 MB (Peak: 1.1098 MB) Zlib enabled. Server Time: 2018-10-21 13:02:34 UTC