Dining room plugs #218335 03/20/17 01:49 PM
Joined: Mar 2005
Posts: 236
watersparkfalls Offline OP
Member
Ok guys you are my go to answer team (much appreciated by the way). So we are doing some apartments and have come across what appears to be gray area in the code regauarding small appliance circuit. Here is a quick synopsis; we have two kitchen that supply only the kitchen, then we have a dining room that also feeds bedroom plugs only (no ceiling light switched receps)...I believe this is a violation as 210.52 lists specifically kitchen, dinining, pantry and simular, with no other outlets, however it was pointed out an exception to outlet in dining room that is a 15a and switched (I'm not sure that applys, but it adds to the confusion). Also some think because we already have the 2 small appliance you can feed whatever you want with dining circuit. Your guy's imput would help, as I said my interpretation is these rooms and simular, which definitely would not include bedroom.

Thanks,
H2O

Last edited by watersparkfalls; 03/20/17 01:52 PM.
2017 / 2014 NEC & Related Books and Study Guides
Re: Dining room plugs [Re: watersparkfalls] #218338 03/20/17 10:34 PM
Joined: Mar 2005
Posts: 236
watersparkfalls Offline OP
Member
two small appliance circuits feeding one kitchen...

Re: Dining room plugs [Re: watersparkfalls] #218339 03/20/17 11:54 PM
Joined: Jul 2004
Posts: 9,558
G
gfretwell Offline
Member
Is this new construction or existing?


Greg Fretwell
Re: Dining room plugs [Re: gfretwell] #218340 03/21/17 07:20 AM
Joined: Mar 2005
Posts: 236
watersparkfalls Offline OP
Member
It is new constructin.

Re: Dining room plugs [Re: watersparkfalls] #218341 03/21/17 10:28 AM
Joined: Jul 2004
Posts: 9,558
G
gfretwell Offline
Member
I hope you caught this at the FEPA/C (pre drywall) because it is a show stopper at least if the AHJ cares about the code.


Greg Fretwell
Re: Dining room plugs [Re: gfretwell] #218344 03/21/17 09:31 PM
Joined: Mar 2005
Posts: 236
watersparkfalls Offline OP
Member
That's what I thought too....easy fix, little money smile


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Admin
Admin
NY, USA
Posts: 3,633
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 18
NORCAL 10
Popular Topics(Views)
274,307 Are you busy
208,148 Re: Forum
195,741 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3