ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat Box
Recent Posts
NEC 2017_392.22(B)(1)(b)
_What's the smallest width

by gfretwell - 09/21/19 11:37 PM
Another weird NEC code question on Feeder Taps
by gfretwell - 09/21/19 11:35 PM
Kichler Lighting Recalls Pendant Lights
by Admin - 09/18/19 08:47 PM
Does a 'normal 3ph-AC motor' include capacitors?
by gfretwell - 09/18/19 01:20 AM
NEC Question_Cord-&-Plug EGC shorter then Neutral
by pcsailor - 09/16/19 05:26 AM
New in the Gallery:
What is this for?
Plug terminals
Who's Online Now
0 registered members (), 7 guests, and 7 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Dining room plugs #218335 03/20/17 02:49 PM
Joined: Mar 2005
Posts: 233
watersparkfalls Offline OP
Member
Ok guys you are my go to answer team (much appreciated by the way). So we are doing some apartments and have come across what appears to be gray area in the code regauarding small appliance circuit. Here is a quick synopsis; we have two kitchen that supply only the kitchen, then we have a dining room that also feeds bedroom plugs only (no ceiling light switched receps)...I believe this is a violation as 210.52 lists specifically kitchen, dinining, pantry and simular, with no other outlets, however it was pointed out an exception to outlet in dining room that is a 15a and switched (I'm not sure that applys, but it adds to the confusion). Also some think because we already have the 2 small appliance you can feed whatever you want with dining circuit. Your guy's imput would help, as I said my interpretation is these rooms and simular, which definitely would not include bedroom.

Thanks,
H2O

Last edited by watersparkfalls; 03/20/17 02:52 PM.
2017 / 2014 NEC & Related Books and Study Guides
Re: Dining room plugs [Re: watersparkfalls] #218338 03/20/17 11:34 PM
Joined: Mar 2005
Posts: 233
watersparkfalls Offline OP
Member
two small appliance circuits feeding one kitchen...

Re: Dining room plugs [Re: watersparkfalls] #218339 03/21/17 12:54 AM
Joined: Jul 2004
Posts: 9,394
G
gfretwell Online Content
Member
Is this new construction or existing?


Greg Fretwell
Re: Dining room plugs [Re: gfretwell] #218340 03/21/17 08:20 AM
Joined: Mar 2005
Posts: 233
watersparkfalls Offline OP
Member
It is new constructin.

Re: Dining room plugs [Re: watersparkfalls] #218341 03/21/17 11:28 AM
Joined: Jul 2004
Posts: 9,394
G
gfretwell Online Content
Member
I hope you caught this at the FEPA/C (pre drywall) because it is a show stopper at least if the AHJ cares about the code.


Greg Fretwell
Re: Dining room plugs [Re: gfretwell] #218344 03/21/17 10:31 PM
Joined: Mar 2005
Posts: 233
watersparkfalls Offline OP
Member
That's what I thought too....easy fix, little money smile


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
sparky66wv
sparky66wv
West Virginia
Posts: 2,236
Joined: November 2000
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Popular Topics(Views)
258,733 Are you busy
194,305 Re: Forum
183,760 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3