submitted by Gregory Madjeski:

Quote
600v, 500kcmil cable termination.


[Linked Image from electrical-photos.com]


Insulated Tools for Electricians

Insulated Tools for Electricians, Installers & Maintenance Technicians

Joined: Apr 2002
Posts: 7,413
Likes: 10
Member
OK, lets start a comment...

Judging by the insulation, and tinned conductor, this is an 'aged' installation.

Hard to tell from the pic, but the clearance from those extra long bolts??

Is the termination (clamp) rated for what appears to be parallel secondaries? Or is this unique engineering??

Is this a POCO transformer?? If so, then throw the NEC out!


John
Joined: Apr 2013
Posts: 22
S
Member
Yes it's an older installation. The transformer is one of 3, single phase Allis-Chalmers "Curvacore" transformers and were used to step down 3 phase 4160V to 208/120V. I did a web search and couldn't find any info on them. All 3 were leaking oil and have been replaced.
Greg

Last edited by sedesigner1; 07/16/14 04:59 PM.
Joined: Jan 2005
Posts: 5,485
Likes: 5
Cat Servant
Member
Leaking oil? Did you, btw, try to soak a paper towel in the oil, then try to set it afire?

Old location .... oil that won't burn ... Hello, PCB's. Not really the sort of thing you simply toss in a dumpster or hose down the drain.

Joined: Apr 2013
Posts: 22
S
Member
They were tagged as PCB free, but I never touched it. There was a service tag on it at least. We were supposed to get an oil sample, but the sampling valve was so corroded we were afraid it would break. I see the same PCB free tags on oil filled utility breakers, but we're replacing those with SF6 dead tank breakers.

Joined: Apr 2002
Posts: 7,413
Likes: 10
Member
OK, now we know 'customer owned', PCB free, a 'mat' setup, and old.

I had a few locations in Union County, NJ that I did demo and bringing the elec into the 20th century. Two locations were PCB issues,confirmed by my samples sent to a lab. The legal disposal was $$$ but necessary and a lot cheaper then dealing with a contamination issue. One of these sites had 'leakers' but thecontamination was limited to the concrete slab and 3' of soil.

Both of the above sites were replaced with POCO 2000KVA pad mounts and respective gear.

BTW, Welcome to ECN Forums from one of the 'Jersey Guys'!!


John
Joined: Apr 2013
Posts: 22
S
Member
Our "leakers" were on concrete so no oil went into soil, but the disposal fee was high (from what I heard). We also replaced the 4160 with a new 12.47KV service & POCO 300KVA 3 phase pad mount and gear. Some of the old stuff I see is almost beyond belief that somebody wasn't killed. Also, thanks for the welcome!
Greg

Insulated Tools for Electricians

Insulated Tools for Electricians, Installers & Maintenance Technicians

Joined: Apr 2002
Posts: 7,413
Likes: 10
Member
You were lucky. Mine seeped thru what was an expansion joint.

I have to find time to look thru my old pics to see if I still have them.

PS:
Look here for a mat job...
https://www.electrical-contractor.n...leries/213689/Copper_Theft.html#comments