Minimum Bend Radius? #213775
07/15/14 07:32 PM
07/15/14 07:32 PM
Admin  Offline
OP
Administrator
Member
Joined: Oct 2000
Posts: 3,503
NY, USA
submitted by Gregory Madjeski:

Quote
600v, 500kcmil cable termination.


[Linked Image]


2017 / 2014 NEC & Related Books and Study Guides
Re: Minimum Bend Radius? [Re: Admin] #213777
07/15/14 10:44 PM
07/15/14 10:44 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,997
Brick, NJ USA
OK, lets start a comment...

Judging by the insulation, and tinned conductor, this is an 'aged' installation.

Hard to tell from the pic, but the clearance from those extra long bolts??

Is the termination (clamp) rated for what appears to be parallel secondaries? Or is this unique engineering??

Is this a POCO transformer?? If so, then throw the NEC out!


John
Re: Minimum Bend Radius? [Re: Admin] #213779
07/16/14 05:58 PM
07/16/14 05:58 PM
S
sedesigner1  Offline
Member
Joined: Apr 2013
Posts: 22
NJ
Yes it's an older installation. The transformer is one of 3, single phase Allis-Chalmers "Curvacore" transformers and were used to step down 3 phase 4160V to 208/120V. I did a web search and couldn't find any info on them. All 3 were leaking oil and have been replaced.
Greg

Last edited by sedesigner1; 07/16/14 05:59 PM.
Re: Minimum Bend Radius? [Re: Admin] #213781
07/16/14 07:03 PM
07/16/14 07:03 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Leaking oil? Did you, btw, try to soak a paper towel in the oil, then try to set it afire?

Old location .... oil that won't burn ... Hello, PCB's. Not really the sort of thing you simply toss in a dumpster or hose down the drain.

Re: Minimum Bend Radius? [Re: Admin] #213784
07/16/14 08:03 PM
07/16/14 08:03 PM
S
sedesigner1  Offline
Member
Joined: Apr 2013
Posts: 22
NJ
They were tagged as PCB free, but I never touched it. There was a service tag on it at least. We were supposed to get an oil sample, but the sampling valve was so corroded we were afraid it would break. I see the same PCB free tags on oil filled utility breakers, but we're replacing those with SF6 dead tank breakers.

Re: Minimum Bend Radius? [Re: Admin] #213785
07/16/14 08:21 PM
07/16/14 08:21 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,997
Brick, NJ USA
OK, now we know 'customer owned', PCB free, a 'mat' setup, and old.

I had a few locations in Union County, NJ that I did demo and bringing the elec into the 20th century. Two locations were PCB issues,confirmed by my samples sent to a lab. The legal disposal was $$$ but necessary and a lot cheaper then dealing with a contamination issue. One of these sites had 'leakers' but thecontamination was limited to the concrete slab and 3' of soil.

Both of the above sites were replaced with POCO 2000KVA pad mounts and respective gear.

BTW, Welcome to ECN Forums from one of the 'Jersey Guys'!!


John
Re: Minimum Bend Radius? [Re: Admin] #213789
07/17/14 03:58 PM
07/17/14 03:58 PM
S
sedesigner1  Offline
Member
Joined: Apr 2013
Posts: 22
NJ
Our "leakers" were on concrete so no oil went into soil, but the disposal fee was high (from what I heard). We also replaced the 4160 with a new 12.47KV service & POCO 300KVA 3 phase pad mount and gear. Some of the old stuff I see is almost beyond belief that somebody wasn't killed. Also, thanks for the welcome!
Greg

Re: Minimum Bend Radius? [Re: Admin] #213795
07/17/14 09:47 PM
07/17/14 09:47 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,997
Brick, NJ USA
You were lucky. Mine seeped thru what was an expansion joint.

I have to find time to look thru my old pics to see if I still have them.

PS:
Look here for a mat job...
https://www.electrical-contractor.n...leries/213689/Copper_Theft.html#comments

Last edited by HotLine1; 07/17/14 09:52 PM.

John

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mxslick
mxslick
Atomic City, ID USA
Posts: 803
Joined: October 2004
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
248,640 Are you busy
186,375 Re: Forum
175,860 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.024s Queries: 15 (0.003s) Memory: 0.9952 MB (Peak: 1.1642 MB) Zlib enabled. Server Time: 2018-08-20 07:02:23 UTC