Existing in-ground pool - 240v pump filter #210991
08/30/13 03:23 PM
08/30/13 03:23 PM
HappyElectrician  Offline OP
Member
Joined: Dec 2011
Posts: 31
Penn USA
A customer of mine has an existing in ground pool. Was there when he bought the house. Recently had an inspection by AHJ for a "Rental Permit" renewal.

Town inspector says it must be GFCI protected.

Problem: It is not cord and plug to pump. There is a sub-panel in basement. 2 pole 240v 15amp breaker. Goes to a switch located at cement slab where pump sits (it is at least more than 6 feet from pool water edge). 12/2 with ground from panel to switch. The 240v pump is hard-wired directly to box where switch is and the pump is bonded to ground. First off the switch is a regular switch and a regular switch cover plate. Should be water proof switch. That part is not too hard to accomplish. But inspector says the circuit must be GFCI protected. How do you protect a 240v pump with a 12/2 wire from the breaker box. My knowledge tells me you need a neutral in order for a GFCI to even function. Am I mmissing something here? Looks like the pump/pool is about 12 years old. Is the pump double insulated; does that make it safe? Normally don't do pool installtions.

Thanks for any suggestions and hints.








Last edited by AFJES; 08/30/13 03:27 PM.
2017 / 2014 NEC & Related Books and Study Guides
Re: Existing in-ground pool - 240v pump filter [Re: HappyElectrician] #210992
08/30/13 06:24 PM
08/30/13 06:24 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,199
Estero,Fl,usa
in 2011 680.21(C) is pretty unambiguous
Quote
(C) GFCI Protection. Outlets supplying pool pump motors
connected to single-phase, 120 volt through 240 volt branch
circuits, rated 15 or 20 amperes, whether by receptacle or by
direct connection, shall be provided with ground-fault circuit interrupter
protection for personnel.



Not a lot of wiggle room

They make 2 pole GFCI breakers for most modern panels and they will work on a L/L load


Greg Fretwell
Re: Existing in-ground pool - 240v pump filter [Re: HappyElectrician] #210994
08/30/13 10:00 PM
08/30/13 10:00 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,950
Brick, NJ USA
As Greg said, NO wiggle room at all

2 pole GFI CBs are available.

You may have to install a new panel or a sun if you can't get a CB


John
Re: Existing in-ground pool - 240v pump filter [Re: HotLine1] #211141
09/19/13 02:25 PM
09/19/13 02:25 PM
HappyElectrician  Offline OP
Member
Joined: Dec 2011
Posts: 31
Penn USA
Sorry for the long delay in my response.

I appreciate your answers. Learned something new. A two pole GFCI breaker will function when no neutral load is connected as long as the pigtail is connected to the neutral bar. Replaced the existing FPE subpanel with anew Square D and new GFCI breaker 240v 15amp and it worked like a charm and passed inspection. I was always taught that you needed the neutral load for them to work properly; oh well learn something new.

Thanks for your time in answering my post


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
TOOL_5150
TOOL_5150
Bay Area
Posts: 61
Joined: August 2007
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
245,931 Are you busy
183,023 Re: Forum
172,782 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.021s Queries: 15 (0.004s) Memory: 0.9615 MB (Peak: 1.0937 MB) Zlib enabled. Server Time: 2018-04-26 05:49:19 UTC