ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat Box
Recent Posts
Any Woodworkers here?
by Bill Addiss - 05/16/21 12:27 AM
Your favourite food?
by Bill Addiss - 05/12/21 05:23 PM
Lock-down Thread
by gfretwell - 05/11/21 12:30 PM
Do You Travel?
by gfretwell - 05/11/21 12:16 PM
Just be aware of this...
by gfretwell - 05/10/21 07:30 PM
New in the Gallery:
2020 - 2021 Winter Project
Garden 2021
Who's Online Now
0 registered members (), 20 guests, and 17 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Existing in-ground pool - 240v pump filter #210991 08/30/13 03:23 PM
Joined: Dec 2011
Posts: 31
HappyElectrician Offline OP
Member
A customer of mine has an existing in ground pool. Was there when he bought the house. Recently had an inspection by AHJ for a "Rental Permit" renewal.

Town inspector says it must be GFCI protected.

Problem: It is not cord and plug to pump. There is a sub-panel in basement. 2 pole 240v 15amp breaker. Goes to a switch located at cement slab where pump sits (it is at least more than 6 feet from pool water edge). 12/2 with ground from panel to switch. The 240v pump is hard-wired directly to box where switch is and the pump is bonded to ground. First off the switch is a regular switch and a regular switch cover plate. Should be water proof switch. That part is not too hard to accomplish. But inspector says the circuit must be GFCI protected. How do you protect a 240v pump with a 12/2 wire from the breaker box. My knowledge tells me you need a neutral in order for a GFCI to even function. Am I mmissing something here? Looks like the pump/pool is about 12 years old. Is the pump double insulated; does that make it safe? Normally don't do pool installtions.

Thanks for any suggestions and hints.








Last edited by AFJES; 08/30/13 03:27 PM.
2017 / 2014 NEC & Related Books and Study Guides
Re: Existing in-ground pool - 240v pump filter [Re: HappyElectrician] #210992 08/30/13 06:24 PM
Joined: Jul 2004
Posts: 9,623
G
gfretwell Online Content
Member
in 2011 680.21(C) is pretty unambiguous
Quote
(C) GFCI Protection. Outlets supplying pool pump motors
connected to single-phase, 120 volt through 240 volt branch
circuits, rated 15 or 20 amperes, whether by receptacle or by
direct connection, shall be provided with ground-fault circuit interrupter
protection for personnel.



Not a lot of wiggle room

They make 2 pole GFCI breakers for most modern panels and they will work on a L/L load


Greg Fretwell
Re: Existing in-ground pool - 240v pump filter [Re: HappyElectrician] #210994 08/30/13 10:00 PM
Joined: Apr 2002
Posts: 7,261
HotLine1 Offline
Member
As Greg said, NO wiggle room at all

2 pole GFI CBs are available.

You may have to install a new panel or a sun if you can't get a CB


John
Re: Existing in-ground pool - 240v pump filter [Re: HotLine1] #211141 09/19/13 02:25 PM
Joined: Dec 2011
Posts: 31
HappyElectrician Offline OP
Member
Sorry for the long delay in my response.

I appreciate your answers. Learned something new. A two pole GFCI breaker will function when no neutral load is connected as long as the pigtail is connected to the neutral bar. Replaced the existing FPE subpanel with anew Square D and new GFCI breaker 240v 15amp and it worked like a charm and passed inspection. I was always taught that you needed the neutral load for them to work properly; oh well learn something new.

Thanks for your time in answering my post


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Grover
Grover
Sebago, ME, USA
Posts: 109
Joined: January 2005
Show All Member Profiles 
Top Posters(30 Days)
Admin 10
Trumpy 7
Popular Topics(Views)
279,176 Are you busy
212,237 Re: Forum
199,252 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3