I am not sure where this post belongs but I am an industrial electrician working in the mining industry. We have ground fault indicator lights on our 3 phase delta system which makes it easier to locate a ground fault issue. . . . one of the trhee lights go out and we just start shutting equipnebt down until we isolate the problem and all three lights are on. Recently we have had a situation where all three lights flicker for several minutes at a time which is something new. I understand the theory ofthe ground fault circuit but am puzzled as to what might cause all three lights to flicker as though there might be some tracking on all three phases. The problem doesn't appear to be isolated to just one transformer in our substation but has been showing up on a couple of different ones. Anyone else have experience with this?
|
|
|
|
Joined: Apr 2002
Posts: 7,412 Likes: 7
Member
|
jmaclean: Good morning & welcome to ECN forums from one of the 'Jersey guys'
John
|
|
|
|
Joined: Jul 2004
Posts: 787
Member
|
A light goes out when that phase gets grounded. The lights go out when there is no power too. Could the flickering ground lights be due to intermintant connections?
|
|
|
|
Joined: Jul 2012
Posts: 4
OP
New Member
|
A light goes out when that phase gets grounded. The lights go out when there is no power too. Could the flickering ground lights be due to intermintant connections? Thanks for the replies, guys. The scenario of the intermittent connections is possible but this occurs in several different MCC's throughout the mill and on at least two subtation transformers.
Last edited by jmaclean; 07/13/12 11:04 AM.
|
|
|
|
Joined: Jun 2004
Posts: 1,273
Member
|
You wouldn't have any VFDs bouncing back harmonic echoes?
====
While there are various ways...
One VFD scheme uses a 'low pass filter' to establish a 'DC tank' -- in the form of a very hefty capacitor, or two... which is then drained by IGBTs to craft AC wave forms by stacking DC transient impedances.
If these massive capacitors cause enough phase shift then the indicator lights would read 'dead.'
A scope or strobe set up would discover if these transitory outages are synch'd to 60Hz or some harmonic. ( 120 Hz = low pass ripple frequency )
Tesla
|
|
|
|
Joined: Jul 2012
Posts: 4
OP
New Member
|
Hmmm... We have dozens of VFD's throughout the mill, most, if not all of them with inductors to filter noise from the system. This just started happening in the last 3 months or so. This is something we haven't considered before.
Last edited by jmaclean; 07/13/12 12:44 PM.
|
|
|
|
Joined: Jul 2012
Posts: 4
OP
New Member
|
Clarification... most of the hve line reactors installed. . .
|
|
|
|
Joined: Jun 2006
Posts: 613
Member
|
Most of the 3 phase ground detectors are using neon lamps. Is it possible you are seeing the normal flickering of neon bulbs? All 3 are going out in Sync? sequentially or random? Is there a set pattern? Any effect on how long it has been on? IE if you turn the power on and the lights flicker for a little while and stop. You turn the power off and on and it starts up again or do you have to turn the power off for a few seconds before it will start again? might indicate a bad capacitor. I am also trying to imagine what normal machine could have a rotating ground fault? Maybe a wire round armature or rotor in a machine?
|
|
|
|
Joined: Mar 2004
Posts: 947
Member
|
Assuming it isn't possible for all three phases to ground at the same time, the other explanation would be power loss. If you lose a phase, do the remaining two bulbs get dimmer?
|
|
|
|
Joined: Jul 2004
Posts: 10,006 Likes: 37
Member
|
I looked on Ebay and they have Dranitz monitors for $100 or less. It can sure help you figure out what is going on with your power. I used mine a lot when I was working for IBM and I took it with me when I left.