Tapping parrellel conductors
#204260
11/22/11 11:17 PM
|
Joined: Apr 2002
Posts: 32
OP
Member
|
Any suggestions on how to tap 4 panels (350MCM each) from 3 parrallel 600MCM feeders in a gutter?
Bill
|
|
|
Re: Tapping parrellel conductors
[Re: sudsy4]
#204263
11/23/11 01:15 AM
|
Joined: Apr 2002
Posts: 7,237
Member
|
'Polaris' type terminations; 600 to 350 range, 7 barrel, or 8 to be safe.
John
|
|
|
Re: Tapping parrellel conductors
[Re: sudsy4]
#204264
11/23/11 10:00 AM
|
Joined: Jul 2007
Posts: 265
Member
|
I am with John on this one. polaris connectors are the way to go, hope it is a BIG gutter!