Posted By: sudsy4 Tapping parrellel conductors - 11/23/11 03:17 AM
Any suggestions on how to tap 4 panels (350MCM each) from 3 parrallel 600MCM feeders in a gutter?
Posted By: HotLine1 Re: Tapping parrellel conductors - 11/23/11 05:15 AM
'Polaris' type terminations; 600 to 350 range, 7 barrel, or 8 to be safe.
Posted By: wire_twister Re: Tapping parrellel conductors - 11/23/11 02:00 PM
I am with John on this one. polaris connectors are the way to go, hope it is a BIG gutter!
Posted By: HotLine1 Re: Tapping parrellel conductors - 11/24/11 02:02 AM
sudsy4:

The 8 barrel Polaris is <11" long, with cable entry from either side. So, you need a troff at least 12".

They make a 'stacker' model also, but...it's not UL Listed.

Check out the link below.

http://www.polarisconnectors.com/pdfs/NSi/IPLD_series.pdf