Any suggestions on how to tap 4 panels (350MCM each) from 3 parrallel 600MCM feeders in a gutter?


Bill
Joined: Apr 2002
Posts: 7,282
Likes: 3
Member
'Polaris' type terminations; 600 to 350 range, 7 barrel, or 8 to be safe.


John
Joined: Jul 2007
Posts: 265
W
Member
I am with John on this one. polaris connectors are the way to go, hope it is a BIG gutter!


Jimmy

Life is tough, Life is tougher when you are stupid
Joined: Apr 2002
Posts: 7,282
Likes: 3
Member
sudsy4:

The 8 barrel Polaris is <11" long, with cable entry from either side. So, you need a troff at least 12".

They make a 'stacker' model also, but...it's not UL Listed.

Check out the link below.

http://www.polarisconnectors.com/pdfs/NSi/IPLD_series.pdf


John

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Posts: 362
Joined: April 2003
Top Posters(30 Days)
timmp 3
Popular Topics(Views)
283,553 Are you busy
216,859 Re: Forum
203,211 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5