Joined: Jan 2005
Posts: 91
H
Member
Any thoughts or experience with this?

Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
My bet is no but the answer will be on the label.


Greg Fretwell
Joined: Jan 2005
Posts: 5,445
Likes: 2
Cat Servant
Member
If the nameplate say 240 .... no, it won't run properly.

If the nameplate REALLY says 230, you can run it at exactly 208. Any voltage drop at all and you're SOL.

If it says 220, you're good to go.

Joined: Nov 2002
Posts: 794
Likes: 3
W
Member
In theory, a boost transformer would solve the problem, by raising the 208V to 240V. Something like this place (no affiliation, others may have better product) http://www.transformeronline.com/buckboost.htm

Being code may be an issue.

Joined: Jun 2004
Posts: 1,273
T
Member
I'm unaware of ANY recent HVAC equipment whose motors couldn't tolerate 200-230 nominal, delivered voltages.

More current will be drawn at the reduced voltage.

The big issue for many HVAC systems is not the motor -- but the control power transformer.

Many are multi-tap -- in which case re-tapping would be most wise.

Unlike the motor, the control logic is pretty finely dialed in.


Tesla
Joined: Mar 2011
Posts: 98
V
Member
Originally Posted by Tesla
I'm unaware of ANY recent HVAC equipment whose motors couldn't tolerate 200-230 nominal, delivered voltages.

More current will be drawn at the reduced voltage.

The big issue for many HVAC systems is not the motor -- but the control power transformer.

Many are multi-tap -- in which case re-tapping would be most wise.

Unlike the motor, the control logic is pretty finely dialed in.


230 rated single phase motors will run at 208 volts, but will probably not last long (more than a few weeks or months) before they burn up.

I'd also question whether a 'window' unit will have any control transformer multi-tap ability, it might though, it seems some of the newer units are dual rated.

Last edited by Vindiceptor; 09/14/11 07:45 PM.
Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
Just my opinion, but...why not just get a window unit that is rated for nominal 208 volts?

Yes, you can install a buck-boost transformer onto the AC circuit back by the panel, but IMHO the labor and materials will probably be $$$ more than another AC; unless we are talking about a really 'big' window unit.



John
Joined: Jun 2004
Posts: 1,273
T
Member
230 rated single phase motors will run at 208 volts, but will probably not last long (more than a few weeks or months) before they burn up.

Virtually all small motors made in the last thirty years will ENTIRELY tolerate 200-230 VAC nominal -- its even on their name-plate.

You have to get into larger ( industrial ) sizes before it's an issue.

And, yes, I've installed 240VAC 1 phase HVAC units where only 208VAC power was available. Six years later the units were still running strong.

The HVAC industry has standards -- one of which is to make it possible to run their equipment at both voltages.

There are NO END of apartments out their receiving two legs of 208Y120 power. Ditto for small businesses.

It is in the nature of small hermetic A/C systems for them to operate entirely surrounded by refrigerant -- and to actively reject their heat to the outside.

Their motors can take it, and take it, and take it.


Last edited by Tesla; 09/14/11 09:37 PM.

Tesla
Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
I just looked a couple up on the internet (LG and Frigidaire) they say 230/208v.

The real answer is going to be on the nameplate of the one in question but it looks like Tesla is right on.


Greg Fretwell
Joined: Mar 2004
Posts: 947
T
twh Offline
Member
I'm with Tesla on this - but I wouldn't even look for taps on a window AC, if they have a transformer. The motor has overload protection and undervoltage probably won't hurt the controls.