stranded wire and devices #201598 06/12/11 11:47 AM
Joined: Aug 2006
Posts: 356
Niko Offline OP
Member
Stranded wires under the device terminals. I know it is not an NEC requirements but i need help finding the answer if it is allowed or not.
I looked in my UL 2010 white book but i wasn't able to find anything.

Is it a manufacturer instruction that stranded wires can not be installed on the devices or UL requirement?

Thanks.


Be kind to your neighbor, he knows where you live

Work Gear for Electricians and the Trades
Re: stranded wire and devices [Re: Niko] #201600 06/12/11 01:16 PM
Joined: Jul 2004
Posts: 9,569
G
gfretwell Offline
Member
Standard devices are listed for stranded or solid wire.

From the White book RTRT

Quote
Terminals of the wire-binding screw, setscrew, or screw-actuated back
wired clamping types are suitable for use with both solid and stranded
building wires.


Greg Fretwell
Re: stranded wire and devices [Re: Niko] #201601 06/12/11 01:58 PM
Joined: Aug 2006
Posts: 356
Niko Offline OP
Member
Unless the instructions state otherwise right?

Last edited by Niko; 06/12/11 02:05 PM.

Be kind to your neighbor, he knows where you live

Re: stranded wire and devices [Re: Niko] #201602 06/12/11 02:21 PM
Joined: Jul 2004
Posts: 9,569
G
gfretwell Offline
Member
I am not sure how the instructions can defy the listing standard and still call themselves listed.
Do you have an example?

I know the back stabs are solid only but this refers to the various styles of screw terminal


Greg Fretwell
Re: stranded wire and devices [Re: Niko] #201603 06/12/11 02:31 PM
Joined: Aug 2006
Posts: 356
Niko Offline OP
Member

From Pass & Seymour:

Side wire accepts #12 #14 AWG solid wire.

For trade master TR receptacle 3232

Last edited by Niko; 06/12/11 02:31 PM.

Be kind to your neighbor, he knows where you live

Re: stranded wire and devices [Re: Niko] #201604 06/12/11 05:41 PM
Joined: Sep 2001
Posts: 806
N
NJwirenut Offline
Member
With stranded wire, I always use the pressure plate type receptacles, or put spade lug crimps onto the conductors for use with the standard screws.

Re: stranded wire and devices [Re: Niko] #201605 06/12/11 06:14 PM
Joined: Jan 2005
Posts: 315
L
luckyshadow Offline
Member
According to the UL white book

Receptacles are listed to use stranded wire as long as it is terminated by one of the following: wire-binding screw, setscrew,or screw actuated back wired clamp type terminal

Switches are not listed to use stranded wire.

Spade lug or fork crimp terminals on the stranded wire is not a listed method for terminating the conductor to the device.

Re: stranded wire and devices [Re: luckyshadow] #201606 06/12/11 08:32 PM
Joined: Jul 2004
Posts: 783
L
LarryC Offline
Member
Does the stranding have to be the standard 19 strand or could it be the extra fine stranding with a strand count of 39 or 51 strands?

Re: stranded wire and devices [Re: Niko] #201608 06/12/11 09:20 PM
Joined: Jul 2004
Posts: 9,569
G
gfretwell Offline
Member
Table 8 specifies the stranding and that fine stranded wire is not it. You really get into this when guys stuff it in a regular set screw lug. You need the kind with a shaped washer on the set screw to catch all the strands and compress them in the lug.


Greg Fretwell
Re: stranded wire and devices [Re: gfretwell] #201609 06/12/11 11:41 PM
Joined: Aug 2006
Posts: 356
Niko Offline OP
Member
Originally Posted by gfretwell
Standard devices are listed for stranded or solid wire.

From the White book RTRT

Quote
Terminals of the wire-binding screw, setscrew, or screw-actuated back
wired clamping types are suitable for use with both solid and stranded
building wires.


I agree, but if the manufacturer states solid only then you have to follow instructions that come with the product. Right?


Be kind to your neighbor, he knows where you live

Page 1 of 3 1 2 3

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Alan Belson
Alan Belson
Mayenne N. France
Posts: 1,803
Joined: March 2005
Show All Member Profiles 
Top Posters(30 Days)
MCosta 3
Popular Topics(Views)
275,386 Are you busy
209,282 Re: Forum
196,579 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3