If the dwelling is using IMC, EMT, AC cable or RMC for the wiring method, is AFCI protection required? or the exception to 210.12 applies to the first receptacle only?
Thank you.
Be kind to your neighbor, he knows where you live
|
|
|
Re: AFCI at the first outlet
[Re: Niko]
#198395
01/20/11 02:14 PM
|
Joined: Jul 2004
Posts: 9,569
Member
|
The last few words sum it up. it shall be permitted to install a combination AFCI at the first outlet to provide protection for the remaining portion of the branch circuit. You still need the AFCI but you can push it out to the first outlet location.
Greg Fretwell
|
|
|
Re: AFCI at the first outlet
[Re: gfretwell]
#198396
01/20/11 03:07 PM
|
Joined: May 2005
Posts: 984
Member
|
I'm also pretty sure that they mean the first receptacle on that circuit, not the first receptacle on that conduit run.
2 circuits = 2 AFCIs.
Ghost307
|
|
|
Re: AFCI at the first outlet
[Re: ghost307]
#198405
01/20/11 10:29 PM
|
Joined: Apr 2002
Posts: 7,233
Member
|
All you have to do then is find the readily available (Ha Ha) AFCI device!!!
John
|
|
|
Re: AFCI at the first outlet
[Re: HotLine1]
#198424
01/21/11 01:56 PM
|
Joined: Feb 2002
Posts: 2,233
Member
|
John,
Has anyone seen an AFCI device? Tooth Fairy? Easter Bunny? ELVIS?
|
|
|
Re: AFCI at the first outlet
[Re: harold endean]
#198426
01/21/11 03:14 PM
|
Joined: May 2005
Posts: 984
Member
|
...and what were they smoking when they saw it??
LOL
Ghost307
|
|
|
Re: AFCI at the first outlet
[Re: ghost307]
#198430
01/21/11 04:27 PM
|
Joined: Jul 2004
Posts: 9,569
Member
|
I see Elvis at the 7-11 all the time and he has lost weight but, alas, no AFCI device.
Greg Fretwell
|
|
|
Re: AFCI at the first outlet
[Re: gfretwell]
#198551
01/26/11 10:47 PM
|
Joined: Jun 2004
Posts: 1,273
Member
|
AFCI devices are in the latest edition of EC Mag.
Tesla
|
|
|
Re: AFCI at the first outlet
[Re: Tesla]
#198559
01/27/11 12:11 PM
|
Joined: Feb 2002
Posts: 2,233
Member
|
Tesla, I am a little behind in my reading. I have 3 EC mag and 4 IAEI mags ahead of the new EC magazine. However I will get there, sooner or later!
|
|
|
Re: AFCI at the first outlet
[Re: harold endean]
#198583
01/28/11 10:36 AM
|
Joined: Apr 2002
Posts: 7,233
Member
|
Tesla:
You said...."AFCI devices are in the latest edition of EC Mag."
IF you mean page 75 of the 1-11 issue....that is the reference materials from the NEC changes/Handbook!
IMHO, and that of many others here....it does NOT exist!
John
|
|
|
|
|