If the dwelling is using IMC, EMT, AC cable or RMC for the wiring method, is AFCI protection required? or the exception to 210.12 applies to the first receptacle only?
Thank you.
Be kind to your neighbor, he knows where you live
|
|
|
|
Joined: Jul 2004
Posts: 10,006 Likes: 37
Member
|
The last few words sum it up. it shall be permitted to install a combination AFCI at the first outlet to provide protection for the remaining portion of the branch circuit. You still need the AFCI but you can push it out to the first outlet location.
Greg Fretwell
|
|
|
|
Joined: May 2005
Posts: 984 Likes: 1
Member
|
I'm also pretty sure that they mean the first receptacle on that circuit, not the first receptacle on that conduit run.
2 circuits = 2 AFCIs.
Ghost307
|
|
|
|
Joined: Apr 2002
Posts: 7,412 Likes: 7
Member
|
All you have to do then is find the readily available (Ha Ha) AFCI device!!!
John
|
|
|
|
Joined: Feb 2002
Posts: 2,233
Member
|
John,
Has anyone seen an AFCI device? Tooth Fairy? Easter Bunny? ELVIS?
|
|
|
|
Joined: May 2005
Posts: 984 Likes: 1
Member
|
...and what were they smoking when they saw it??
LOL
Ghost307
|
|
|
|
Joined: Jul 2004
Posts: 10,006 Likes: 37
Member
|
I see Elvis at the 7-11 all the time and he has lost weight but, alas, no AFCI device.
Greg Fretwell
|
|
|
|
Joined: Jun 2004
Posts: 1,273
Member
|
AFCI devices are in the latest edition of EC Mag.
Tesla
|
|
|
|
Joined: Feb 2002
Posts: 2,233
Member
|
Tesla, I am a little behind in my reading. I have 3 EC mag and 4 IAEI mags ahead of the new EC magazine. However I will get there, sooner or later!
|
|
|
|
Joined: Apr 2002
Posts: 7,412 Likes: 7
Member
|
Tesla:
You said...."AFCI devices are in the latest edition of EC Mag."
IF you mean page 75 of the 1-11 issue....that is the reference materials from the NEC changes/Handbook!
IMHO, and that of many others here....it does NOT exist!
John
|
|
|
Posts: 8,443
Joined: July 2002
|
|
|
|