Anyone know of an approved product that can be used to repair broken/separated flexible metallic conduit? I have a 4" flex with 500mcm feeders to switchgear with the flex broken. So I am hoping I can repair in place without shutdown, remove,replace flex, repull, reterminate, etc etc.
|
|
|
|
Joined: Apr 2002
Posts: 7,382 Likes: 7
Member
|
Jay:
There is no product that I know of for what you described.
Looks like an R&R job
John
|
|
|
|
Joined: Jul 2004
Posts: 9,931 Likes: 34
Member
|
The first question would be how was it separated in the first place. You may have a physical damage problem that precludes FMC. I have seen people weave this stuff back together but I still would not try it hot. This was not uncommon under computer room floors. I even had a picture in the IAEI magazine of that. Joe T may still have it on his web site in the violations area.
Greg Fretwell
|
|
|
|
Joined: Jun 2004
Posts: 1,273
Member
|
Such damage, presumably within the Electrical Room, is very disturbing.
I rather suspect that the flex was buckled during the original installation.
Alternately, the custodian/owner has been stacking 'stuff' on top of the flex until failure.
We've all seen it: the E Room becomes the closet to jamb everything under the sun for the custodian.
I see an R&R in your future.
Tesla
|
|
|
|
Joined: Mar 2007
Posts: 404
Member
|
|
|
|
|
Joined: Jul 2005
Posts: 183
OP
Member
|
It was likely due to installation damage since its location makes it unlikely to be hit. It was a little tedious but I was able to wind it back together since it was fairly close to the connector, which saved quite a bit of grief. I knew there were approved kits to repair in use underground conduit, so I was fishing for something similar for flex. thanks for the feedback - i will save the duct tape repair idea for another time.
|
|
|
Posts: 61
Joined: August 2007
|
|
|
|
|