ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 255 guests, and 16 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Feb 2004
Posts: 115
H
Haligan Offline OP
Member
Connected 2 Cree 4" LED cans to dedicated circuit. Powered on, checked placement and operation. Switch off, breaker off.
Come back almost an hour later. Test with voltage pen to make sure no one warmed anything up while I was away. Surprise- there's voltage. Woah.

I put the meter on the hot and neutral of the lights and there is a steady 63v trickling back down from the two lights.

I then disconnected hot, neut, and gnd from circuit. Nothing but the two LED cans.
Still the 63 phantom volts.

What's happening here? It sounds like capacitance draining backwards.

I didn't think to put the ammeter on there.

Joined: Jun 2004
Posts: 1,273
T
Member
Use analog meter...

Voltage will disappear.



Tesla
Joined: Feb 2004
Posts: 115
H
Haligan Offline OP
Member
I had no idea. Too much trust in all things digital.