Joined: May 2005
Posts: 15
OP
Member
|
Thanks for the info, the power co is coming back to look at the pole connections. Forgive me what is a logger I have never heard that term. Mike
dukes
|
|
|
|
Joined: Jun 2006
Posts: 34
Member
|
Maybe not the correct term , you hook it to the lines for say 24 hours and it gives you a line graph of the voltage over time .
|
|
|
|
Joined: Jul 2004
Posts: 9,932 Likes: 34
Member
|
The Dranitz I have uses a set point for spikes and sags, logging anything that exceeds that point.
Greg Fretwell
|
|
|
|
Joined: Jul 2004
Posts: 9,932 Likes: 34
Member
|
If this is a regular occurrence, you might do as well with a simple analog meter. It is really hard to do much with a digital meter unless it will save the low point. Even then you don't know if that was just a spike or a real sag. The analog meter is far more visual.
Greg Fretwell
|
|
|
|
Joined: Jul 2002
Posts: 8,443 Likes: 3
Member
|
If this is a regular occurrence, you might do as well with a simple analog meter. It is really hard to do much with a digital meter unless it will save the low point. Even then you don't know if that was just a spike or a real sag. The analog meter is far more visual. I agree Greg, I have an elderly analouge meter here that has the facility to set the needle at centre scale and it has +/- values printed on the scale. In some cases, I actually prefer the analogue meter to a digital one, especially if the readings are all over the place or changing to any great degree. Having said all that I also own a data logger, it's handy to be able to leave the thing behind (behind the panel dead-front, of course) and go and get it say two days later and see what it has recorded. It's told me a few interesting stories to date.
|
|
|
|
Joined: Jul 2004
Posts: 9,932 Likes: 34
Member
|
When I first got my Dranitz I set it up at what I thought was a reasonable level in my office on Friday and came back the next Monday to see how I was doing. It had run out of paper.
Greg Fretwell
|
|
|
|
Joined: Jul 2002
Posts: 8,443 Likes: 3
Member
|
When I first got my Dranitz I set it up at what I thought was a reasonable level in my office on Friday and came back the next Monday to see how I was doing. It had run out of paper. Blast!!, you would say.
|
|
|
|
Joined: Apr 2002
Posts: 7,382 Likes: 7
Member
|
Greg said... "It had run out of paper"
That's one of the reasons I bought a digital Amprobe Digimatic I had the analog Amprobe chart recorders also, and remembering to have someone replace the chart roll was a pain.
Dranetz was a tool the computer guys used to love!
John
|
|
|
|
Joined: May 2005
Posts: 15
OP
Member
|
Hi all Power co came, said they checked all connections at trans. pole. Customer still has blinking lights. My digitial meter only shows slight changes in voltage less than 2%. I can not isolate the problem, shut breakers feeding anything with a motor or compressor and it still blinks. The lights only dime intermittenly.
dukes
|
|
|
|
Joined: Jul 2002
Posts: 8,443 Likes: 3
Member
|
I think this is definitely a local problem and not part of the PoCo network. What really needs to be ascertained, is how the lights are wired in that place. If them lighting circuits are all sharing a common feed, I would suspect a dodgy neutral (or phase) connection somewhere in the installation. More than likely on one of the lighting circuit home-runs. An ohm-meter and a long piece of wire would help speed the fault-finding process up.
Mike, you never mentioned if the receptacle circuits were affected by this intermittent voltage sag problem. Were these checked at the same time?, as that would also give you some sort of indication as to where the fault could be.
Hope this is of some help.
|
|
|
Posts: 806
Joined: October 2004
|
|
|
|