240.21 (B) 2 Taps not over 25feet .?? #186182 04/24/09 09:24 PM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline OP
Member
3 conditions must be complyed with.
But as I read it theres nothing saying that the disconnect at 25 ft has to be in the same room over even same floor , long as conductor distance does not exceed the 25feet.
You guys read it the same??
Yoopers

2017 / 2014 NEC & Related Books and Study Guides
Re: 240.21 (B) 2 Taps not over 25feet .?? [Re: Yoopersup] #186199 04/26/09 09:26 PM
Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
I agree, 25ft of conductor is the only 'physical' limitation.

Re: 240.21 (B) 2 Taps not over 25feet .?? [Re: JBD] #186209 04/27/09 10:28 AM
Joined: Dec 2000
Posts: 4,281
electure Offline
Member

I don't see the possible benefit of having the disconnect in the same room as the tap, or on the same floor.

After all, it won't deenergize the tapped conductors.






Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
AllClear
AllClear
Belmond Iowa US
Posts: 44
Joined: August 2005
Show All Member Profiles 
Top Posters(30 Days)
sparky 10
Popular Topics(Views)
259,730 Are you busy
195,067 Re: Forum
184,473 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3