3 conditions must be complyed with.
But as I read it theres nothing saying that the disconnect at 25 ft has to be in the same room over even same floor , long as conductor distance does not exceed the 25feet.
You guys read it the same??
Yoopers

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
I agree, 25ft of conductor is the only 'physical' limitation.

Joined: Dec 2000
Posts: 4,289
Member

I don't see the possible benefit of having the disconnect in the same room as the tap, or on the same floor.

After all, it won't deenergize the tapped conductors.






Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
BEAMEUP
BEAMEUP
WA
Posts: 27
Joined: December 2004
Top Posters(30 Days)
NORCAL 3
Robski 1
Popular Topics(Views)
288,013 Are you busy
220,140 Re: Forum
206,133 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5