Posted By: Yoopersup 240.21 (B) 2 Taps not over 25feet .?? - 04/25/09 01:24 AM
3 conditions must be complyed with.
But as I read it theres nothing saying that the disconnect at 25 ft has to be in the same room over even same floor , long as conductor distance does not exceed the 25feet.
You guys read it the same??
Yoopers
Posted By: JBD Re: 240.21 (B) 2 Taps not over 25feet .?? - 04/27/09 01:26 AM
I agree, 25ft of conductor is the only 'physical' limitation.
Posted By: electure Re: 240.21 (B) 2 Taps not over 25feet .?? - 04/27/09 02:28 PM

I don't see the possible benefit of having the disconnect in the same room as the tap, or on the same floor.

After all, it won't deenergize the tapped conductors.