by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 3,789 guests, and 19 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 2 of 2 1 2
electure #182594 12/03/08 08:46 PM
Joined: Dec 2001
Posts: 444
S
Sandro Offline OP
Member
Tried hooking in the pressure switch control at different points in the control circuit. Same issue as o.p.

This was a customer supplied push button starter. I normally don't use these types for air compressors, and thought there would be a simple way without extensive rewiring, or adding extra parts/contacts/switches to keep the push buttons functional.

As others above have noted, the off/auto switch is what we normally use and best.




Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

Sandro #182600 12/03/08 10:19 PM
Joined: Nov 2005
Posts: 826
Likes: 1
J
Member
If you need to keep your 2 buttons, the cheapest way that will work safely is to add 1, DPDT control relay.
1.) Wire "L" or "Hi" to N.C. "OFF" button to N.O. "ON" Button to relay coil to OLs to "N" or "Lo"
2.) Wire relay N.O. contact in parallel with the "ON" button. (Holding contact for the control ckt.)
3.) Wire "L" or "Hi" to other N.O. relay contact to P-switch with differential to contactor coil. (Normal compressor cycling when control circuit is active.
Add any E-stop switches to Line 1. Just about any starter assembly should have the volume to add a control relay. I can do the ladders up on CADD if you want.
Joe

Joined: Mar 2004
Posts: 947
T
twh Offline
Member
I don't think you can do this with a 3 wire stop/start unless you add a relay.

A simple toggle switch in a handy box will do to switch the control circuit. It isn't a lot of money.

twh #182602 12/04/08 01:17 AM
Joined: Nov 2005
Posts: 826
Likes: 1
J
Member
Here is the partial ladder with the rotary selector switch and indicator.
Joe

Attached Images
COMPCTL1.JPG
Joined: Nov 2005
Posts: 826
Likes: 1
J
Member
Option 2 partial ladder, using a control relay to keep existing buttons.
Joe

Attached Images
COMPCTL2.JPG