electure #182594 12/03/08 08:46 PM
Sandro Offline OP
Tried hooking in the pressure switch control at different points in the control circuit. Same issue as o.p.
This was a customer supplied push button starter. I normally don't use these types for air compressors, and thought there would be a simple way without extensive rewiring, or adding extra parts/contacts/switches to keep the push buttons functional.
As others above have noted, the off/auto switch is what we normally use and best.
Sandro #182600 12/03/08 10:19 PM
If you need to keep your 2 buttons, the cheapest way that will work safely is to add 1, DPDT control relay.
1.) Wire "L" or "Hi" to N.C. "OFF" button to N.O. "ON" Button to relay coil to OLs to "N" or "Lo"
2.) Wire relay N.O. contact in parallel with the "ON" button. (Holding contact for the control ckt.)
3.) Wire "L" or "Hi" to other N.O. relay contact to P-switch with differential to contactor coil. (Normal compressor cycling when control circuit is active.
Add any E-stop switches to Line 1. Just about any starter assembly should have the volume to add a control relay. I can do the ladders up on CADD if you want.
Joe
twh Offline
I don't think you can do this with a 3 wire stop/start unless you add a relay.
A simple toggle switch in a handy box will do to switch the control circuit. It isn't a lot of money.
twh #182602 12/04/08 01:17 AM
Here is the partial ladder with the rotary selector switch and indicator.
Joe
Option 2 partial ladder, using a control relay to keep existing buttons.
Joe