1,014
22
Posts: 10,031 Likes: 37
That could just be open delta wired wye primary. Actually pretty normal here using 2 transformers. One of the transformers is center tapped on the secondary and off you go. I can get a picture of that at the "shop and rob" at the end of my street.
Yah, I've seen that 2 transformer connection very often. But those transformers are usually connected to a 4 wire wye system with a grounded neutral. I found a picture of a transformer like I was asking about: http://www.electricalphotos.com/showphoto.php/photo/425/ppuser/28This picture is very similar to the one I seen in that other book. Could it be a three phase unit or not?
I don't think I've ever seen a US pole mounted three phase transformer before in real life. (Post those pics guys  ) Okay, I happened to catch one in the background of a pic I took today (yes of traffic lights). ![[Linked Image from electricalphotos.com]](http://www.electricalphotos.com/data/500/thumbs/100_7075.JPG) Closeup of single transformer: ![[Linked Image from electricalphotos.com]](http://www.electricalphotos.com/data/500/thumbs/100_7083.JPG) Ian A.
Re: 3 phase rectangular pole mounted transformers.. Ya usually the PoCo will use 3 separate cans for a 3 phase service drop to a large building but it is NOT uncommon to see a single 3phase transformer of 150 KVA or less on a pole. Usually I have seen them where a building is an older one and had a separate 3 phase service strictly for an elevator or other motor driven equipment.
Don't worry fellas, I am working on those pix still. I know where there is a nice brand-new installation of one of these transformers, right outside my friends 7'th floor balcony.. I will have them in the next few days!
I have never seen 2 transformers wired wye secondary. It is usually red leg delta around here.
Yah, I've seen that 2 transformer connection very often. But those transformers are usually connected to a 4 wire wye system with a grounded neutral. I have never seen 2 transformers wired wye secondary. It is usually red leg delta around here. Sorry I should have been more clear. I meant to say the Primary is wye connected.(each transformer is connected phase to neutral). Yes the secondary is open delta with a high leg.
10-4 That sounds regular here. I will try to remember my camera tomorrow.
This is the label on a 50KVA like the one at the top of this thread. ![[Linked Image from esteroriverheights.com]](http://esteroriverheights.com/electrical/50_kva_label.jpg)
The 50 KVA up close ![[Linked Image from esteroriverheights.com]](http://esteroriverheights.com/electrical/50_kva_transformer.jpg)
Here is an American open delta setup with a 3-wire (no MGN) primary. Grounding is done by local rod at the pole. This particular setup is in the high desert area in Sothern California Edison territory where I noticed that most, if not all of the local distribution, was done with no MGN and the transformers connected L-L. This would be considered unusual by US standards which is mostly MGN distribution. ![[Linked Image from i286.photobucket.com]](https://i286.photobucket.com/albums/ll106/electricman277/DSC00329.jpg)
Peter
