1 members (Scott35), 582 guests, and 35 robots.
#173496 01/10/08 10:48 PM
Can someone tell me if there is a rule in the CEC that mentions the partition between the main breaker compartment and the rest of the breakers in a panel board
Thanks
Doug
The only rule I could quickly find that states this (somewhat) is 6-306(a):
"Consumer's service raceways shall
(a) contain only the consumer's service conductors..."
If it's for service equipment it must be marked "approved for service entrance", so a barrier will come with that approval.
Sixer
Sixer #173504 01/11/08 12:00 AM
Thanks that what i found too.
Rules 6-306 & 6-212 make mention of it in a round abouts way.
This was my original question to Doug via a private message. I have heard that the panels used in Canada are designed with a cover arrangement that permits access to the load side breakers and bus without exposing you to the line side terminals on service equipment. If this is true I think that it is a great safety idea and would like to start the process of making such a requirement in the NEC. I guess I have two questions. Is your service equipment designed as I stated above? If so what code or standard requires this?
Doug, thanks for helping out with this question.
Some panels. I can't speak for all have a two part panel cover. One part covers the main and the second part covers the breakers.
Doug, do you have a copy of Part 2 of the CEC? Could be some additional rules in there that can help you out.
jay8 #173610 01/14/08 04:56 PM
No I dont have part2 have part one and the CD for the cost of the CD they should put part 2 on it too.:(
This is where I assume we find it in Part 2
Canadian Standards Association
Panelboards: C22.2 #29
