Can someone tell me if there is a rule in the CEC that mentions the partition between the main breaker compartment and the rest of the breakers in a panel board Thanks Doug
|
|
|
Re: Service Equipment
[Re: dougwells]
#173502
01/10/08 10:58 PM
|
Joined: Aug 2005
Posts: 265
Member
|
The only rule I could quickly find that states this (somewhat) is 6-306(a): "Consumer's service raceways shall (a) contain only the consumer's service conductors..."
If it's for service equipment it must be marked "approved for service entrance", so a barrier will come with that approval.
Sixer
"Will it be cheaper if I drill the holes for you?"
|
|
|
Re: Service Equipment
[Re: Sixer]
#173504
01/10/08 11:00 PM
|
Joined: May 2003
Posts: 1,155
OP
Member
|
Thanks that what i found too.
|
|
|
Re: Service Equipment
[Re: dougwells]
#173509
01/11/08 08:20 AM
|
Joined: Aug 2007
Posts: 10
Member
|
Rules 6-306 & 6-212 make mention of it in a round abouts way.
|
|
|
Re: Service Equipment
[Re: CanuckSparky]
#173593
01/14/08 07:22 AM
|
Joined: Nov 2000
Posts: 2,148
Member
|
This was my original question to Doug via a private message. I have heard that the panels used in Canada are designed with a cover arrangement that permits access to the load side breakers and bus without exposing you to the line side terminals on service equipment. If this is true I think that it is a great safety idea and would like to start the process of making such a requirement in the NEC. I guess I have two questions. Is your service equipment designed as I stated above? If so what code or standard requires this?
Doug, thanks for helping out with this question.
Don(resqcapt19)
|
|
|
Re: Service Equipment
[Re: resqcapt19]
#173608
01/14/08 02:48 PM
|
Joined: Aug 2002
Posts: 402
Member
|
Some panels. I can't speak for all have a two part panel cover. One part covers the main and the second part covers the breakers.
|
|
|
Re: Service Equipment
[Re: dougwells]
#173609
01/14/08 03:39 PM
|
Joined: Jul 2005
Posts: 183
Member
|
Doug, do you have a copy of Part 2 of the CEC? Could be some additional rules in there that can help you out.
|
|
|
Re: Service Equipment
[Re: jay8]
#173610
01/14/08 03:56 PM
|
Joined: May 2003
Posts: 1,155
OP
Member
|
Doug, do you have a copy of Part 2 of the CEC? Could be some additional rules in there that can help you out. No I dont have part2 have part one and the CD for the cost of the CD they should put part 2 on it too.:(
|
|
|
Re: Service Equipment
[Re: dougwells]
#173611
01/14/08 03:58 PM
|
Joined: May 2003
Posts: 1,155
OP
Member
|
This is where I assume we find it in Part 2 Canadian Standards Association Panelboards: C22.2 #29
|
|
|
Re: Service Equipment
[Re: dougwells]
#173612
01/14/08 04:06 PM
|
Joined: May 2003
Posts: 1,155
OP
Member
|
|
|
|
|
|