Hospital emergency power circuit #170851 11/13/07 09:12 PM
Joined: Oct 2001
Posts: 172
W
watthead Offline OP
Member
I need some input from those with experience in hospital wiring. I have been asked to install some receptacles in the patient care rooms in the emergency room. The receptacles are for new computer interface equipment, and are to be installed on the wall aproximately six inches from the ceiling. They also want them on emergency / generator power. My question is whether the health care facility mc cable is adequate for the installation, or would emt be required?

Thanks for your input.

2017 / 2014 NEC & Related Books and Study Guides
Re: Hospital emergency power circuit [Re: watthead] #170855 11/13/07 09:19 PM
Joined: Jan 2004
Posts: 1,498
G
George Little Offline
Member
Your choice- either would satisfy 517. They probably will need the redundant ground. I would look an see what the print calls out. Don't mean to be an educated donkey here but the plans have the last word.


George Little
Re: Hospital emergency power circuit [Re: George Little] #170858 11/13/07 09:39 PM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline
Member
I;d advise you to Read 517.30 C (3) Handbook explains it well.

Re: Hospital emergency power circuit [Re: Yoopersup] #170859 11/13/07 09:49 PM
Joined: Jan 2004
Posts: 1,498
G
George Little Offline
Member
Ernie- He can add 517.13 to the answer too.


George Little
Re: Hospital emergency power circuit [Re: George Little] #170862 11/13/07 10:00 PM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline
Member
George
517.30 C (3) refers you to 517.13A & 517.13 (B)
But it also lists only 4 areas where Listed Flexable Metal raceways CAN be used. 517.30 C (3)(3)

Re: Hospital emergency power circuit [Re: Yoopersup] #170869 11/13/07 10:51 PM
Joined: Jan 2004
Posts: 1,498
G
George Little Offline
Member
Thanks Ernie- I learned something.


George Little
Re: Hospital emergency power circuit [Re: Yoopersup] #170871 11/13/07 10:57 PM
Joined: Oct 2001
Posts: 172
W
watthead Offline OP
Member
Thanks guys. I had looked at both of those Code sections, but was still not exactly sure if I could sneak the HCF-mc in under 517.30(C)(3)(3)c. I am now looking for my handbook. There are no plans or drawings on this one, only a quick walk thru with we want one here and here,and I am supposed to remember the 18 or is it 19 locations. thanks again.

Re: Hospital emergency power circuit [Re: watthead] #170876 11/13/07 11:25 PM
Joined: Oct 2001
Posts: 172
W
watthead Offline OP
Member
It looks like I will be using emt on this one to cma. Hospital says they don't care which way as long as it is done to code.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
richard
richard
L.I. New York
Posts: 99
Joined: August 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 6
Popular Topics(Views)
258,623 Are you busy
194,210 Re: Forum
183,684 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3