I'd guess the red and black go to the permanent panel inside the house; when the temp is no longer needed, this panel will be removed and the red and black lines will be pulled into the meter can. They are taped up so they won't accidentally touch anything.
The lack of bushings around the red and black is to give the next guy a head start on stripping the insulation.
|
|
|
|
|
Joined: Sep 2007
Posts: 12
Member
|
The old SE cable has been cut off at the lintel...don't have a guess why it's in the panel. BTW the meter was live but not for long. After about four attempts, the owner finally got a licensed contractor. As for the inside, this house was a fire job (wonder why) with new walls, trusses and etc.
Last edited by Raymfl; 09/24/07 08:48 PM.
|
|
|
|
|
Joined: Sep 2007
Posts: 12
Member
|
The outlet box wasn't secured to the wal.
|
|
|
|
|
Joined: Dec 2000
Posts: 4,294
Member
|
Ray, welcome  Do you suppose that the black and red conductors through that sharp hole are intended to be connected to the mechanical lugs bus-tapped into the bottom of the panel? Scary
|
|
|
|
|
Joined: Jun 2007
Posts: 50
Member
|
Installations like this bring to mind the old ceremonies for drumming a disgraced officer out of the corps....
I can see it now:
Assembled in the town square, neatly lined up, are all the AHJ's, Licensed Contractors, Journeymen .... and, with the best view, the apprentices.
The accused is paraded forth. His Carhartt's are removed, to be replaced by some poly-cotton jumpsuit. His electrical tools are, one by one, dropped into a vat of molten metal. His hands are liberally coated with Gorilla Glue, then inserted into his pockets. Finally, his hard hat is replaced with a funnel.
Then the disgraced is taken to a soup kitchen, nearest the bus station. Good Riddance. You forgot some other potential audience members: The POCO linemen, the local FD, and IEEE members! I see a Darwin Award candidate in the making here folks!
|
|
|
|
|
Joined: Nov 2001
Posts: 745
Member
|
I don't understand why this was done. With nearly the same amount of effort, the proper sized conductors could have been installed. Never mind what I would consider a poor job of landing the poco conductors on the line side of the meter.
Two things I observe about the load conductors from the main disco/sub panel to the panel somewhere inside the house; 1) The neutral conductor is way too short to reach the buss at the top of the panel and would have to be spliced, and 2) the three conductors (red, black and bare) don't appear to pass through any kind of conduit fitting, or even a clamp of some sort. Please correct me if I am wrong, but isn't there supposed to also be a separate grounding conductor from this main/sub panel to the panel inside?
I have seen numerous panels like this in my part of the world, primarily for mobile home service poles, where the main conductors to the home land in those bottom lugs, and another couple of breakers are supplied for such purposes as a water well pump, outbuildings, etc.
Mike (mamills)
|
|
|
|
|
Joined: Sep 2007
Posts: 12
Member
|
Those taped conductors go nowhere...they were cut where they exit the wall and there was no panel in the house. Again, this was a fire job and the inside was totally gutted. It is allowed to build the service with a GFCI outlet below for temporary use, but must be complete except for branch circuits and panel feeders. This is an example of an owner builder who is way over his head.
Ray
Last edited by Raymfl; 09/25/07 04:50 PM.
|
|
|
|
|
Joined: Nov 2001
Posts: 745
Member
|
Thanks, Ray. Somehow, I missed your posts above.
Mike (mamills)
|
|
|
|
|
Joined: Nov 2005
Posts: 507
Member
|
hell, it was only temporary...what's the big deal? 
|
|
|
|
|
Joined: Sep 2007
Posts: 12
Member
|
It was very temporary. Our juristiction requires that a TUG be complete, then have a pre-power before the feeders can be energized.
|
|
|
Posts: 109
Joined: January 2005
|
|
|
|