IBC 1006.3.5 (exterior egress emergency lighting) #154405
07/09/05 02:15 PM
07/09/05 02:15 PM
G
GamecockEE  Offline OP
Member
Joined: Jul 2004
Posts: 49
Georgetown, SC 29440
I have run up on this requirement in a couple of jurisdictions (SC) on projects I have worked on. It doesn't seem to be universally enforced, as say the other 4 provisions of IBC 1006.3. Kind of wondering if that was the observation of you folks out there. Also wondering what is being used for egress illumination outside of buildings for small & medium sized commercial buildings. Manufacturer names will do. thanks for your insights in advance

Building Codes & Related References
Re: IBC 1006.3.5 (exterior egress emergency lighting) #154406
07/09/05 09:29 PM
07/09/05 09:29 PM
R
Ryan_J  Offline
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
I require this whenever it applies. What I have been seeing is an outdoor rated (wet location) bugeye type of light. I don't know the manufacturer of the product, as I have never had to buy one. [Linked Image]


Ryan Jackson,
Salt Lake City
Re: IBC 1006.3.5 (exterior egress emergency lighting) #154407
07/19/05 06:02 PM
07/19/05 06:02 PM
B
boggerbutt2454  Offline
Member
Joined: Feb 2005
Posts: 44
Concord NC USA
Prescolite (Hubbell), Chloride, Lithonia all make remote heads for outside as well as weather emergency fixtures just to name a few.

Re: IBC 1006.3.5 (exterior egress emergency lighting) #154408
07/19/05 07:54 PM
07/19/05 07:54 PM
R
Ralpha494  Offline
Member
Joined: May 2004
Posts: 73
Pewaukee,WI,USA
This week the inspector cited us for not having either a dual head or dual filaments on the single head. New one on me. I guess I'll put up dual heads from now on. It seems to make sense to have it that way, so you can see outside if one is out.

Re: IBC 1006.3.5 (exterior egress emergency lighting) #154409
07/22/05 06:33 PM
07/22/05 06:33 PM
R
raider1  Offline
Member
Joined: Jul 2005
Posts: 46
north logan, utah, US
One thing to keep in mind is NEC 700.12 (E).

This says " The branch circuit feeding the unit equipment shall be the same branch circuit as that serving the normal lighting in the area and connected ahead of any local switches."

Chris.

Re: IBC 1006.3.5 (exterior egress emergency lighting) #154410
07/23/05 06:38 PM
07/23/05 06:38 PM
G
GamecockEE  Offline OP
Member
Joined: Jul 2004
Posts: 49
Georgetown, SC 29440
Thanks for your insights and answers. I have spent some time looking to see if I could see some egress fixtures located outside. Can't say that I have to be honest with you folks, but they may have battery back-up internal to the fixture.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
UTEE87 1
Popular Topics(Views)
257,168 Are you busy
192,983 Re: Forum
182,648 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.017s Queries: 14 (0.004s) Memory: 0.9772 MB (Peak: 1.1237 MB) Zlib enabled. Server Time: 2019-07-21 23:19:45 UTC