IBC 1006.3.5 (exterior egress emergency lighting) #154405 07/09/05 02:15 PM
Joined: Jul 2004
Posts: 49
G
GamecockEE Offline OP
Member
I have run up on this requirement in a couple of jurisdictions (SC) on projects I have worked on. It doesn't seem to be universally enforced, as say the other 4 provisions of IBC 1006.3. Kind of wondering if that was the observation of you folks out there. Also wondering what is being used for egress illumination outside of buildings for small & medium sized commercial buildings. Manufacturer names will do. thanks for your insights in advance

Building Codes & Related References
Re: IBC 1006.3.5 (exterior egress emergency lighting) #154406 07/09/05 09:29 PM
Joined: Aug 2003
Posts: 1,374
R
Ryan_J Offline
Moderator
I require this whenever it applies. What I have been seeing is an outdoor rated (wet location) bugeye type of light. I don't know the manufacturer of the product, as I have never had to buy one. [Linked Image]


Ryan Jackson,
Salt Lake City
Re: IBC 1006.3.5 (exterior egress emergency lighting) #154407 07/19/05 06:02 PM
Joined: Feb 2005
Posts: 44
B
boggerbutt2454 Offline
Member
Prescolite (Hubbell), Chloride, Lithonia all make remote heads for outside as well as weather emergency fixtures just to name a few.

Re: IBC 1006.3.5 (exterior egress emergency lighting) #154408 07/19/05 07:54 PM
Joined: May 2004
Posts: 73
R
Ralpha494 Offline
Member
This week the inspector cited us for not having either a dual head or dual filaments on the single head. New one on me. I guess I'll put up dual heads from now on. It seems to make sense to have it that way, so you can see outside if one is out.

Re: IBC 1006.3.5 (exterior egress emergency lighting) #154409 07/22/05 06:33 PM
Joined: Jul 2005
Posts: 46
R
raider1 Offline
Member
One thing to keep in mind is NEC 700.12 (E).

This says " The branch circuit feeding the unit equipment shall be the same branch circuit as that serving the normal lighting in the area and connected ahead of any local switches."

Chris.

Re: IBC 1006.3.5 (exterior egress emergency lighting) #154410 07/23/05 06:38 PM
Joined: Jul 2004
Posts: 49
G
GamecockEE Offline OP
Member
Thanks for your insights and answers. I have spent some time looking to see if I could see some egress fixtures located outside. Can't say that I have to be honest with you folks, but they may have battery back-up internal to the fixture.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 69
Joined: January 2002
Show All Member Profiles 
Top Posters(30 Days)
Admin 23
GeneSF 8
Popular Topics(Views)
257,893 Are you busy
193,629 Re: Forum
183,251 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3