Electricians revenge
0 members (), 205 guests, and 12 robots.
#140996 06/04/04 08:36 PM
Wenborg — US/ANSI standard C84.1-1995 has ~22 60Hz entries 120-1,100,000V. Available in PDF format for a fee at places like http://global.ihs.com/doc_detail.cfm?item_s_key=00008289
[This message has been edited by Bjarney (edited 06-04-2004).]
#140997 06/05/04 02:51 PM
This is what I know in my neck of the woods (rural Ontario Canada), MV is distributed at 44KV Delta (sometimes in pairs, it is not uncommon to see six 44KV lines along major routes), that go directly to large industry, or substations down to 4-7 KV Wye (4KV for urban, 7KV for rural), either single, 3, or sometomes even 2/3 phases.
#140998 06/06/04 06:57 AM
Austria is simple. 230/400V, 50Hz +/- 1%. MV IIRC usually 15kV, HV 110(?), 230 and 400kV. Distribution of anything exceeding 400V are a delta arrangement.
Note on Germany: from what I was told recently in some remote areas 230V delta supplies w/o neutral may still be encountered.
#140999 06/06/04 11:41 AM
C-H Offline
Below is a copy of an e-mail I sent Wenborg
Hi!
I have taken the freedom to duplicate my reply in the thread on ECN. This to open it to public scrutiny and correction.
There are a large number of questionable pieces of information in my list. Unfortunately, it is almost impossible to get the information verified. Much of the 230 vs. 220V/240V confusion is likely to stem from the fact that IEC has recommended 230V as the standard voltage for 50 Hz systems for many years. Even if utilities in many countries use is it today, they rarely have a campaign to tell the world. Unless voltage tolerances are strict, you leave the old transformers set to 220/240V and set the new to 230V.
>We have compared your list of available voltages and ours. There are several discrepancies. We
>have verified ours and ask that you recheck yours that do not match. Please let us know your
>findings. The list below are the countries in question.
I'm interested in how you have verified your list.
I have put I "No reference" for the countries where I have no reference, other than Steve Kroplas website or a single source of questionable credibility. I'm afraid the nice formatting in your message is lost when I reply.
>Country Your List Our List
>Algeria 133/230/230/400 127/220
No reference.
>Andorra 230 220/240
Andorra is between Spain and France and too small to be part of CENELEC, but it will almost certainly follow the same standard as Spain and France.
>Austria 230/400 220/380
230/400V is correct. The EU / CENELEC members switched to 230V 1 Jan 1995.
> Belgium 230/400 127/220/380/
230/400V. Belgium also has the old 127/220V system in use, but today only the phases are used and the voltage is nominally 230V.
> Botswana 230/400 220/380
No reference.
>Bulgaria 230/400 220/380
If it hasn't already changed to 230V it will do so in the future, as it is set to become a member of EU in 2007 and it is already an associate member of CENELEC.
>Cambodia 230/400 120/220/380
>Congo Republic 230/400 220/380
No reference.
>Croatia 230/400 230/380
230/380V is impossible as the phase to phase voltage is always 1.73 times the phase to neutral voltage in a wye system. Yes, I know you know that [Linked Image]
>Cyprus 230/400 220\240\
The utility (there's only one) still lists 240/415V as the nominal voltage. I changed my list to 230/400V recently as Cyprus joined Cenelec on 1 Feb and the EU on 1 May 2004. This puts it in the common market and Cyprus has to accept 230/400V equipment.
>Czech Republic 230/400 220\400\
230/400V. Member of the EU from 1 May 2004.
>Denmark 230/400 220\240\380\
230/400V. See comment under Austria.
>Falkland Islands 240/415 220/240/380
I have tried to find information on this. 240/415V is merely an educated guess, not a fact.
>French Polynesia 220/380 120\127\220\
>Gambia 230/400 220\380\
No reference.
>Greece 230/400 220/380
>Guadeloupe 230/400 220/380
French overseas department. I have no reference for a change to 230V, but it is likely [Linked Image]
>Iceland 230/400 220/380
230/400V. See comment under Austria. (I could give you a reference in Icelandic [Linked Image] )
>India 240/415 220/230/380
>Indonesia 230/400/127/220 127/220/380
No reference.
>Ireland 230/400 220/380
230/400V See comment under Austria.
>Isle Of Man 230/400 240/415
This is a small island between Britain and Ireland. Officially independent, it has strong ties to the UK and gets its power from an underwater line from the British mainland. Likely to use 230/400V as everyone around them do.
>Italy 230/400/ 220/380
>Jordan 230/400 220/380
I have found no source to confirm the 230V. Go with 220/380V.
>Laos 230/400 220/380/
The only reference I have is a contact with a utility engineer working in Laos.
>Latvia 230/400 220/380/
I was in contact with the Latvian standards organisation last year. They were in the process of adjusting to 230V.
>Lebanon 230/400 110/220/380
The Lebanese power system was wrecked in the civil war and has been rebuilt in the 90's after Syria invaded. Apparently it was rebuilt to the same standard as in Syria (i.e. the European system) 220/380V or 230/400V.
>Libya 127/220/230/400 230/400
No reference.
>Liechtenstein 230/400 220
See the comment under Andorra. Lichtenstein is located between Switzerland and Austria. In addition it is a member of EFTA and thus part of the common market in Europe.
>Lithuania 230/400 220
230/400V or will soon be. Member of the EU from 1 May 2004.
>Luxembourg 230/400 120/208/220/380
See the comment under Austria.
>Macao 220/380 230/400
My list is now reads 230/400V.
>Malta 230/400 240/415
I was in contact with the standards org. in Malta last year. According to them, the nominal voltage was changed from 240/415V to 230/400V in 2002.
>Mongolia 230/400 127/220/380
>Myanmar - Burma 230/400 220
>Nepal 230/400 220/400
No reference.
>Netherlands 230/400 220/380
>Northfolk Island 240/415 230/400/
>Panama 110/120/240 110/115/120/220/230/240/
No reference.
>Philippines 125/216/220 110/120/220/230/
You are more likely to be correct.
>Poland 230/400 220/380
>Portugal 230/400 220/380
>Romania 230/400 220/380
See comment under Bulgaria.
>Rwanda 230/400 220/380
No reference.
>Samoa 230/400 240/400
No reference. 240/400V is impossible. :-)
>San Marino 230/400 220/240
230/400V or maybe 230V. It's a small country in the middle of Italy.
>Senegal 133/230 230
No reference, but 230V is probably the correct one.
>Slovakia 230/400 220/380
230/400V or will be. Member of the EU from 1 May 2004.
>Slovenia 230/400 220/380
>Solomon Islands 240/415 220
I know I found it listed as 240/415V somewhere. I really should have made a list of references.
>Timor-Leste 230/400 220/240
The electrical system is being rebuilt/improved by international, in particular Australian, help after the Indonesians left. I don't think the nominal voltage matters, as the capital suffers from rolling blackouts. The team working on the power system have a webpage with the schedule somewhere. You could e-mail them. (Again, I should have made a list of references)
>Trinidad 115/230/230/400 115/220/380
>Tunisia 220/380/230 127/220/380
No reference.
>Turkey 230/400 220/380
No reference at hand.
>Tuvalu 240/415 60Hz 220 50Hz
This one has caused me some headache. As is the case with many a small island, trustworthy information is almost impossible to find.
>United Kingdom 230/400 230/415
230/400V. The law that changed to voltage from 240/415 to 230/400V can be found on line. And of course, 230/415 is an impossible voltage [Linked Image]
>Vanuatu 240/415 230
See the comment under Tuvalu.
>Vietnam 127/220/380 120/127/220/380
I think I had a reference for this. (I really, really should have written the sources down!)
>Virgin Islands, British 110 220
>Virgin Islands, U.S. 110 120/240
No reference.
Regards,
Clas-Henrik
[This message has been edited by C-H (edited 06-06-2004).]
#141000 06/06/04 04:15 PM
I can state nothing definite to what has already been stated, but I'll add a few extra thoughts on some of those entries.
A former French colony in North Africa, so 127/220 and 220/380 are quite likely in the past. If they've raised the 220 specification to 230, then it's possible that any old 127/220 systems (now maybe with only phase-to-phase loads) have been re-specified as 133/230.
British territory, so it's quite likely that they standardized at 240/415 and have now adopted 230/400. I cannot confirm though.
Agreed. The French DOMs (Department Outre Mer) are considered a part of France itself officially, so the official French 230/400 standard would probably be adopted automatically. Ditto the nearby island of Martinque, also a French DOM.
I've seen some references which indicate India still has 250/433 in places, as well as 3-wire DC services. I get the impression that there is yet to be full standardization across the country.
A small country less than the size of Rhode Island. 120/208 is most likely a misquote. It's more likely that the old lower-voltage systems were 127/220 like neighboring France and Belgium.
It seems hard to get reliable information on the many Caribbean nations. There are odd variations from what one might expect, e.g. British territories like Bermuda using 120V at 60Hz and some places using 120V with American fittings but at 50Hz.
For many of these poor African countries the voltage regulation is so poor that it probably doesn't make that much difference whether it's nominally 220 or 230V.
#141001 06/07/04 09:13 AM
Wenborg Offline OP
I want to thank everyone for all the comments. They are all very helpful. The information you have provided does answer some of the questions of why there are so many discrepancies.
Any additional verification anyone can provide will be greatly appreciated.
#141002 06/07/04 01:07 PM
In the above data, Wenborg, why is there no mention of Australia, South Africa, Madagasgar or New Zealand?.
[This message has been edited by Trumpy (edited 06-07-2004).]
#141003 06/07/04 01:11 PM
Luxembourg 120/208
That's a joke isn't it? Tell me it's a mistake or a joke!
Possibly @60Hz too? *shaking head in disbelief*
Liechtenstein doesn't even generate their own power, their grid is supplied from the Swiss power company. Or maybe it was the Austrian. In either case it should be 230/400V, 50Hz.
#141004 06/07/04 05:21 PM
Wenborg Offline OP
Several countries were not mentioned because there seemed to be total agreement on them. If you have information that you know is accurate on any country please include it. The countries listed were the ones that are very inconsistent in people’s lists.
For Luxembourg I have 230/400V 50Hz
For Liechtenstein I have 230/400V 50Hz
#141005 06/07/04 05:33 PM
I should have added that the U.K. also uses the 110V for building-site power tools, the same as DJK described for Ireland.
Just to clarify the situation, there is no main PoCo distribution at these lower voltages. Building sites simply use a portable transformer which steps down the incoming supply from our standard LV level to either:
(a) a single-phase center-tapped 110V supply, so that each line is at 55V to ground, or
(b) on large sites a 3-phase transformer running a 64/110 wye secondary with all tools connected phase-to-phase.
There are also odd uses of "foreign" systems outside their normal region in places which aren't really in any country at all. For example, some of the North Sea oil rigs are apparently wired entirely to U.S. standards.