499
11
never mind ...excuse me !!!
[This message has been edited by johnd24 (edited 07-26-2003).]
Johnd24, 300.4(A)(1) does not require a listed plate. The code only requires that the plater be made of steel that is at least 1/16" thick. A blank cover meets this rule. -------------- I like the Slater boxes too. ![[Linked Image]](https://www.electrical-contractor.net/ubb/smile.gif)
Peter
Johnd24,just curious,whats not neat about Sparky's work besides the unusual armor job?
Russell
[This message has been edited by ga.sparky56 (edited 07-25-2003).]
johnd24, please tell me you are not an inspector. If you are please tell me you will stay in Ohio.
yes Al, it is a P&S box w/internal clamps, they have the most volume per 1G i can find on the market.
johnd24, 'neat workmanship' is such a grey area, the single gang in question violates a bona fide code, it is visual, cite it and be the thread king!
~S
I see a hint in in order..... the 1G box is in violation of the very code that sells (and is written on the package) of the stacker beside it.... btw~ this is post & beam construction
Sparky are you saying that by the time the wires enter the box,they are too close to the edge of the stud? ![[Linked Image]](https://www.electrical-contractor.net/ubb/confused.gif)
ding>ding>ding we have a winner! yes ga.sparky56 ! (this calls for a copy/paste) (D) Cables and Raceways Parallel to Framing Members. In both exposed and concealed locations, where a cable- or raceway-type wiring method is installed parallel to framing members, such as joists, rafters, or studs, the cable or raceway shall be installed and supported so that the nearest outside surface of the cable or raceway is not less than 32 mm (11/4 in.) from the nearest edge of the framing member where nails or screws are likely to penetrate. Where this distance cannot be maintained, the cable or raceway shall be protected from penetration by nails or screws by a steel plate, sleeve, or equivalent at least 1.6 mm (1/16 in.) thick
I,m afraid to ask what the prize is. ![[Linked Image]](https://www.electrical-contractor.net/ubb/biggrin.gif)
As a guy who doesn't do houses, isn't this a problem(1.25 in clearances) on any interior wall where a box is installed?? like between 2 bedrooms or wherever a stud wall is used a partition. If the box is 3 inches deep on a 3.5 wall?????