#100917 01/22/07 10:50 AM
Joined: Jan 2007
Posts: 6
S
skipper Offline OP
Junior Member
what is the best way to tap the entrance cable at the meter socket ? also my second panel is 50 ft away do i need to have a disconect just after the meter ?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#100918 01/22/07 11:20 AM
Joined: May 2002
Posts: 1,716
R
Member
Will your POCO even allow the second meter on this one drop or lateral?

Roger

#100919 01/22/07 11:40 AM
Joined: Jan 2007
Posts: 6
S
skipper Offline OP
Junior Member
the women i talked to at NStar told me that since i had a 200amp service and was only adding a 100 amp panel that i could just tie into the existing meter and add the second meter. I dont know i dont do res. work. before i talked to the inspector i figure i get some info

#100920 01/22/07 12:31 PM
Joined: May 2002
Posts: 1,716
R
Member
Is this a lateral or overhead service?

Is NStar your POCO?

Roger

#100921 01/22/07 12:39 PM
Joined: Jan 2007
Posts: 6
S
skipper Offline OP
Junior Member
NSTAR IS MY POCO and it is and over head with a 4/0 service drop to the first meter

#100922 01/22/07 12:53 PM
Joined: Jan 2005
Posts: 5,445
Likes: 2
Cat Servant
Member
4/0 wire .... well, we're not talking about wire nuts here!

In similar situations, I instal a gutter in the service drop, before the meters. There, I make my splices, using NSI / Polaris set screw connectors. The PoCo has no problem with adding a seal to the gutter.

[Linked Image]

[This message has been edited by renosteinke (edited 01-22-2007).]

#100923 01/22/07 01:53 PM
Joined: Jan 2007
Posts: 6
S
skipper Offline OP
Junior Member
boy that helps thanks!

#100924 01/22/07 03:08 PM
Joined: May 2002
Posts: 1,716
R
Member
Now, for the rest of your question, both panels will need disconnecting means grouped together on the exterior of the building. If the existing panel already has a disconnect at the meter you will only need to supply one for the new panel.

Read 230.72

Roger

#100925 01/22/07 10:47 PM
Joined: Mar 2004
Posts: 814
B
Member
reno, does the poco require you to supply the sealable screwheads?

#100926 01/22/07 11:25 PM
Joined: Jan 2005
Posts: 5,445
Likes: 2
Cat Servant
Member
The gutters made by Hoffman come with a small hasp that will accept a seal.