I'm working on a condo for the owner and we noticed that the common wall has no outlets/switches on it. This wall is about 15 feet long in the master bedroom.
Is there a code that prohibits an outlet on this wall? Condo is approximately 20 years old and in Sacramento, CA.
Could be related to fire rating of the common wall (usually 1HR) or have to do with the legal seperation of the units since one person would own 1 layer of sheetrock and 1/2 of the 2x4...
I can see it now... my lawyer needs to talk to your lawyer about your romex that you have running through my half of the 2x4...
It's probably a fire-rated wall and they didn't want to go to the extra expense of adding receptacles and then restoring the fire rating. Fortunately; there is no place in the Code that says that the requirements are waived if someone is too cheap to meet them.
boxes shall not be installed on opposite side of walls or partitions of staggered stud construction unless "Wall Opening Protective Materials" are installed according to the requirements of their Classification.
And I also agree that this does not eliminate the requiremnts of 210.52.
Typically UL fire barrier separation walls has verbage that says boxes on opposite sides of the wall need some kind of fire separation. The distance used in many assemblies is 24 inches apart to say that the boxes are not back to back.
There is no good reason why the receptacles are not installed.
If sound was the issue, they make putty pads. Putty pads are also used to achieve the fire rating separation.