cpal...I would interpet 680.26(C)(3) as follows,

When a "permanently installed" swimming pool is installed a equipotential bonding grid shall be established and it shall extend 3 feet horizontally from the water.

Connect this grid to the parts specified in 680.26(B)...which is basicly all other metalic parts and equipment associated with the pool.

Even with a fiberglass inground pool a grid must be installed.

So, I also would have to establish a bonding grid around a permanently installed pool which is above ground and surrounded with a grass lawn border.

Hopefully somebody comes out with an easier way to construct such a grid than 680.26(C)(3)b.

The purpose is to pick up any stray voltage that may be present.

Also, I'm not sure if the "mesh" commonly installed in a concrete deck pour is an acceptable method of establishing a grid...680.26(C)(1)describes reinforcing rods bonded together.?

shortcircuit