Alan,
Quote
After the umpteenth time of reading about the concrete encased electrode IF 20 feet of #4 bare is used in the footer it becomes the concrete encased electrode and connection to the rebar is NOT required.
The installation of the copper does not make the rebar go away. The code section requires the rebar to be used as a grounding electrode if it is there. If both are there they both must be used.
Don


Don(resqcapt19)