JG, 250-24(A)1 doesn't say first to the disconnect, " any accessible point from the load end of the service drop or service lateral to and including the terminal or bus to which the grounded service conductor is connected at the service disconnect." Why would you want to take another wire out to the meter socket when the socket is already bonded to the grounded conductor?