250.24(A)(1) says "any accessible point from the load end of the service drop or service lateral to and including the terminal or bus to which the grounded service conductor is connected at the service disconnecting means."
The meter base is accessible, you don't destroy the building finish when you open it.
I didn't like the connection in there either but the handbook shows it as one of the acceptible locations.


Greg Fretwell