Curt,
the voltages mimic a standard center tapped delta like this , i have 120/240 and a high leg of somewhere around 190 v's

how it is done with 2 x-formers i really can't say.....

and yes, you can meter voltage under a load bettween fence~GEC

as a matter of fact, i did up a new GEC in the pumphouse, and one can see (and even hear) a nice fat blue spark on removing/connecting it under said load.

i'm going back soon to install a nema3r stop/start, so maybe i'll probe it out for the sake of the thread.....

so we thus ajourn to 250.6(b)and items 1 thru 4

stumped? me too, i'm going out of my way to drag the state insp. there, i'll post his advice.

ps~ yes ThinkGood, i'm scrathin' like a hound here, but what father would'nt brave the wilderness given the request of a 'marshmallow stick' for his 11 yr old?