Sorry, this is still from the '99 NEC:

410-4(d) states that "No parts of cord connected fixtures, hanging fixtures, lighting track, pendants or ceiling-suspended (paddle) fans shall be located within a zone measured 3 ft. horizontally and 8 ft. vertically from the top of the bathtub rim or shower stall threshold..."

410-57(c) states that "A receptacle shall not be installed within a tub or shower space..." which I'm left to assume "space" is defined above in 410-4(d),

630-41(c) states that "Switches shall be located at least 5 ft., measured horizontally, from the inside walls of the spa or hot tub..."

550-8(f)(1) "Shower or Bathtub Space Receptacle outlets shall not be installed in or within reach (30 inches) of a shower or bathtub space."

Any differnce in the 2002?

My 2002 book is in the truck and my feet are killing me after two 13 hour days... (Excuses, excuses...)