Ian, Scott, Larry,
Thank you all for your input.

Scott- Yes, two 60v, two-wire outputs, with a maximum 105 amps available from each. I have no intentions of using 120v.

Larry, your description of my set-up is precisely what I am doing.
I anticipated my output capacity to be cut in half to about 12.5 kva, which is very adequate for my application.
I will run a split, balanced load, at 60v.

Probably more than you want to know, but:
(I initially planned 120v in series through all my elements. My understanding of molybdenum heating elements, and real-world practice, is that they run best at lower voltages and high amperages. (there might be an arcing problem, or something. I don't know) Thus, the decision to split the series.

Their resistance is so low that they are almost at a dead short when cold, with resistance rising with the temperature, so I will run a phase-angle fired SCR with Current Limit to control them. The Watlow SCR is designed for transformer-coupled loads. The furnace is capable of 3000 Deg.F but will be idled at 1800F-2200F with 2400F maximum.)


Doug